Discuss RCD Tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

EddieB

-
Arms
Reaction score
27
I was called out to a friends the other day he was experiecing the RCD trip problem you know the one, it trips you reset, 1 hr later it trips again you reset it, 3hrs later etc etc . I had a look at the circuits and found a ring that was down to .1 of a Meg Iinvestigated further and found the problem to be an anti surge multi plug the kind the PC, Printer etc plugs into. After unplugging it the readings went to >100meg, he had 2 in the house different makes but about the same readings. Could this have been the offending item (s) and has anybody else experienced this problem with this kind of product
 
hi
It's probably the neon on the extention lead? Giving you those readings. Its not going to trip a RCD though, not unless you have loads of PCs and monitors, more than lightly its a appliance connected to the circuit.
Regards
 
It was a low reading to earth not between, The neon is across the L & N I dont think the earth is involved other than what goes on inside the multiplug that causes it to be surge resistant.
 
Hi


If the is low reading is to earth and then its the oxide varistor in side the surge unit. My advise would be don't test with surge units connected as your likely to damage them and get very low readings. These units can go faulty and give a leakage to earth. Did you try the ramp test on your RCD? Just to make sure it's not a sensitive one..


Regards
 
Len, It's a very busy three bed house with no guide to show me around I unplugged what I could find and started delving into cupboards and walldrobes after I found the low reading.
Electro I did ramp test and it tested out fine
thanks guys
 
It was a low reading to earth not between, The neon is across the L & N I dont think the earth is involved other than what goes on inside the multiplug that causes it to be surge resistant.

The problem may be that one of the surge components which is connected from L-E breaking down.
 
Surge protection shunts spikes (over-volts) to earth. Insulation testing generally squirts 500V into the cct doesn't it? Most of that is going to be seen as a surge and go through the MOV and give a low Ohm reading?As always I am ready to be shot-down but isn't it more likely/possible that a faulty Switch-mode PSU in a PC or such like is dumping onto the earth to cause the RCD trip?
 
Last edited by a moderator:
Surge protection shunts spikes (over-volts) to earth. Insulation testing generally squirts 500V into the cct doesn't it? Most of that is going to be seen as a surge and go through the MOV and give a low Ohm reading?As always I am ready to be shot-down but isn't it more likely/possible that a faulty Switch-mode PSU in a PC or such like is dumping onto the earth to cause the RCD trip?

Most PC's filter circuits are connected to earth but should be approx 3.5mA which is not enough to cause RCD to trip, could be surge components breaking down now and again if it is not constantly tripping but at different times.
 
Most PC's filter circuits are connected to earth but should be approx 3.5mA which is not enough to cause RCD to trip

Yr right that only about 3.5mA leakage should be present but bad design, low quality components, component filure, etc. could all contribute to an increased current to earth. What if the dialectic were breaking down at some peak value?

could be surge components breaking down now and again if it is not constantly tripping but at different times.

Could be but then again the surge components are usually MOV and semiconductors tend to break 'once and for all' rather than 'now and then' no matter what Schroedinger said about his cat.

My monies still on SP causing low ohm, SMPSU causing the RCD trip and STD's causing an itchy scrot.
 
I was called out to a friends the other day he was experiecing the RCD trip problem you know the one, it trips you reset, 1 hr later it trips again you reset it, 3hrs later etc etc . I had a look at the circuits and found a ring that was down to .1 of a Meg Iinvestigated further and found the problem to be an anti surge multi plug the kind the PC, Printer etc plugs into. After unplugging it the readings went to >100meg, he had 2 in the house different makes but about the same readings. Could this have been the offending item (s) and has anybody else experienced this problem with this kind of product
Hi Eddie,
Did removal of you anti surge plug stop your tripping?
 
When doing an insulation resistance test in a domestic It is worthwhile adding as a matter of habit one more test to the recommended
Do a 230 volt between lives and earth and between lives to be sure the circuit you are testing is actually neon and appliance free.
This gives assurance that you will not damage sensitive electronic equipment that may have been overlooked for isolating by applying the 500 volt initially

If the insulation resistance tests are sound,then the rcd function is sound
Reconnect the electrocic equipment and retest the rcd on the non trip scale

Whilst most are concentrating on the anti surge readings being perhaps the problem I very much doubt that this is the case
The possibility is that an item such as a fridge freezer or such as earth leakage problems with stat controlled functions
Have you also insulation tested the household appliances for any low
neutral earth readings, Items that may have been left plugged in during the tripping episodes
These may not be enough on their own to cause the tripping ,but when left plugged in with heavier loads applied, they could be the culprit

Intermittent tripping is unfortuately the biggest nuisance for the householder and the spark to deal with
 
It has not occured since, so it makes you wonder.

Des 56
it was the first thing I did,I always go through with 250v if I'm not sure if I missed anything that may be plugged in
 
Last edited:

Reply to RCD Tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
424
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock