Hello all
i have just installed a mini consumer unit next to an old board to protect d/s sockets And lights for some kitchen work ll ok for 2 days but customer called me out sockets tripping any ideas no o/s light all sockets un plugged IR over 200 meg r1 very high tho need to check tightness of none cations in morning
if rcd sets with mob off is it live to earth fault?
Any ideas could be boiler yet to disconnect
cheers
 
OP
P

piz

Sorry Trev meant to say checking tightness of sockets and calculations tomoz ie r1 r2 and r n and IR tests but sure all ok
 

joe j

Regular EF Member
Messages
68
Poss faulty rcd, give it a ramp test, but most likely a faulty appliance. But I bet 'there was nothing plugged in, it just went off'
 
OP
P

piz

Yeah your right what am I looking or on ramp test it's on my meter but never used it
every item un plugged still won't re set
 
OP
P

Plonker 3

If you are taking the customers word on nothing being plugged in, then I would ask them when you get there as sometimes they feel a little daft that something they have done is causing this too happen. Although as you say it could well be the boiler.
 

trev

Regular EF Member
Right so I'm guessing you've installed a 2w RCD CU for the work you have done and the RCD is tripping after a few days. Am I right so far?
You say the sockets are tripping but are you absolutely sure it's that circuit that is causing the trips?
Now you say you're going to check your test results tomorrow but what is making you doubt them?
Were there any issues before you did what you did?
Here's a cruncher for you, if all your test results were fine then you have to ask what has happened since you left the job. Leaks, spillages, new (faulty) appliance?
Maybe it's the boiler but I'd be asking the client some searching questions, how is the boiler fed, from the RFC or independently?
 

sparks1973

Regular EF Member
Messages
1,027
Location
Leeds
well whilst your checking connections behind fronts....check the terminations in the C/U n all.....loose connections can/will cause an RCD to let go....
 

soulman

Electrician's Arms
Messages
364
Location
Durham
I would defo check for loose connections, 3 electricians to a property where rcd was tripping, nobody found the fault, blamed on appliance (though this normally the case). Neutral in ccu was just sitting on top of main switch not gripped at all, once secured no more tripping.:smiley2:
 

sparks1973

Regular EF Member
Messages
1,027
Location
Leeds
I would defo check for loose connections, 3 electricians to a property where rcd was tripping, nobody found the fault, blamed on appliance (though this normally the case). Neutral in ccu was just sitting on top of main switch not gripped at all, once secured no more tripping.:smiley2:
and if it wasn`t a loose connection found....would you just `blame it on an appliance` then eh?....ever heard of a ramp test?....
 

soulman

Electrician's Arms
Messages
364
Location
Durham
yes of course i have heard of a ramp test and very rare a rcd fails a ramp test in my opinion. i am trying to be helpful with suggestions, unlike your useless unprovoked comment. The customer states nothing is plugged in & rcd wont reset so how are you going to perform a ramp test EH!!
 

Deleted member 9648

Mentor
Electrician's Arms
Trainee Access
Messages
5,575
Location
south uk
???....You said the board serves sockets and lights....how do you know it's the sockets tripping the RCD and not the lights?.....

Edited due to not reading the OP correctly!
 
OP
P

piz

2way board lights stay on sockets trip when mob switched on
 
OP
D

drew35

I think everybody that answered the OP deserves a round of applause for doing so.

i cant make sense posts like this no punktuation nor grammer makes wonder what appening skools this days but kidz should thank lucky starz exams arnt ritten anymore all theyd all be down job center
 

marcusone

Electrician's Arms
Messages
158
Location
Bristol
Bit harsh Drew. I think the UK has the best edumacation system in the southern hemisphere :)

Sent from my HTC One X using Tapatalk 2
 
OP
P

piz

Thanks to everyone for the help especially you drew not lol.
I have now changed the RCD and all is fine
 