hi guys ,several pieces of equipment on different circuits on the non rcd side side of a split main/rcd board are tripping the rcd .the mcbs
are not tripping.

any ideas as to why this is happening? could it be crossed neutrals or just a faulty rcd.thanks
 
disconnect all items on circuits, this may include outside lights, pond pumps etc and then see if rcd trips. aafter doing this start thinking about ir test and faulty rcd.

ps don't leave pump off for too long
 
Are you sure you've connected the neutrals to the correct bars?

More to the point when was the board last working properly and who's been meddling!
 
Sounds like a crossed neutral to me but I don't understand why it should start all of a sudden or is it a new installation?????

Have you just started using an immersion heater perhaps?
 
Has the client wire up any plugs?
I had a situation where the RCD kept tripping and the microwave plug had been wired neutral to earth, earth to neutral.
Thought at first that the circuit cable had been damaged.
 
Just to confirm do you mean that the circuits on the non-rcd side are tripping the RCD??

I take you have isolated the MCBs on the RCD side and still getting tripping there - you could have a low resistance on the N/E of the RCD side - try an IR test N/E on the RCD side then look for borrowed neutrals as that could also trip the RCD.

Also when did this start?? what happened? is it a new build/rewire/new cu??? All these would point to the CU not being wired correctly.

Also what state is CU in?? (the wires)
 

Reply to rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
553
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock