I am testing a residential consumer unit with an RCD that is tripping daily at different times. With a multimeter set on the 2ΩM I tested each individual fuse after switching off mains switch and RCD and out of the 10 fuses 8 gave me a reading of 0.4 between earth and phase. I am assuming that the insulation resistance of wires in the installation is very poor causing the tripping of the RCD!
 
hello welcome
you cant do insulation tests with a multimeter you need an ins res tester to induce voltage onto the circiut
it sounds like you may need some help with your testing


Even so 0.4 ohms is still low between phase & earth

NRG ~ I suggest you turn on each breaker one at a time just to see if you get an instanteaneous trip, that may at least isolate which circuit the fault is on. ~ make sure you are not putting yourself or others at risk whilst doing so If you do have an earth fault!
 
Last edited:
Even so 0.4 ohms is still low between phase & earth

NRG ~ I suggest you turn on each breaker one at a time just to see if you get an instanteaneous trip, that may at least isolate which circuit the fault is on. ~ make sure you are not putting yourself or others at risk whilst doing so If you do have an earth fault!

Wheres the injected 500v? doesnt happen on a multimeter! as soon as multimeter was mentioned it was wrong.

Multimeters can be good for fault finding but not insulation testing.


NRG114 if your are testing phase to earth have you disconnected the neutral as you may be getting a path through equipment still coneected.
 
Last edited:

Reply to RCD tripping in the Australia area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
519
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock