Discuss rcd tripping in the UK Electrical Forum area at ElectriciansForums.net
C
craigday
I recently got called to a rcd kitchen circuit tripping, so I removed all appliances as normal but still tripped so carried out IR test which showed no fault? any ideas no fault found?
IR test again at 1000V. but make sure nothing is plugged in.
trapped cable behind an accessory or a nail in cable.. these faults don't always show uo on IR tests. ambient temperature fluctuations cause expansion and contraction, thus the fault is there 1 minute and gone the next. just a case of using the old eyeballs more than relying on test gear.
if it's been working up, to now, that can be discounted. i would be looking for pictures hung above sockets before anything else.
Reply to rcd tripping in the UK Electrical Forum area at ElectriciansForums.net
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...