This is a problem that happens quite regurarly and it happens with diffrent appliances so i assume it is not a faulty appliance and also any socket. e.g You could be watching the tv and then the toaster would get turned on and trip the breaker or vce versa

I was wondering what you guys think the problem could be whether there is too much on and trips it?

Could i up the size of the breaker(32A)?

any1 have suggestions on how to overcome this?
 
Last edited by a moderator:
This is a problem that happens quite regurarly and it happens with diffrent appliances so i assume it is not a faulty appliance and also any socket. e.g You could be watching the tv and then the toaster would get turned on and trip the breaker or vce versa

I was wondering what you guys think the problem could be whether there is too much on and trips it?

Could i up the size of the breaker(32A)?

any1 have suggestions on how to overcome this?


what other circuits are on the rcd

who fitted the rcd board and how long ago any test results

what size breaker they on now
 
what other circuits are on the rcd

who fitted the rcd board and how long ago any test results

what size breaker they on now

Not sure what other circuits on it as only been phoned about it,

dont know who fitted board

its a 32a socket crcuit

Can you confirm it is an rcd tripping not an mcb or is it an rcbo unit?


It is the RCD main switch that trips all the time

Could it b a faulty RCD main switch?
 
Last edited by a moderator:
I suggest if you have the test gear you clamp the main earth and measure the leakage if you can measure mA scale if not do you have a ramp test facility on your meters and just test the rcd on its own with no outgoings on it then test with outgoings this way you can work out what leakage is present if any.
If the above isnt an option maybe diconnecting each circuit in turn for a day both live and neutral to see if the nuisance tripping stops on any particular circuit.
As a pointer water heaters, showers are prone to leakage with age or anything else with a heating element, also outside light fitting letting in rain just check weather when it trips.
 
ive found this b4 and it was an immersion heater on its way out try isolating this remember neutral as well as live see if this helps.
 
I've found that the old-style RCD main switches ( big greenish boxes with the yellow push test button ), if they haven't been operated for sometime, and then are operated, they can inherit a fault that when the supply is under load, it'll trip out the RCD.

Solution was to replace the old RCD with a new one in an enclosure. That sorted the problem out !!!!!
 

Reply to RCD tripping? in the Australia area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
514
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
266
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock