but it's not relevant here as there wasn't a hard short. The socket outlet and the washing machine got sprayed with water, which is not conductive enough for a wet fitting to leak 46A
Hold on a minute, are you trying to tell me that you wont get a dead short from water? and it doesn't have to be 48 amps, as the circuit itself would already have a load on it that is at near full capacity.
What do you think we relied on before RCD's?

You crazy UK leco's should brush up on both your practicle and theory.
 
Hold on a minute, are you trying to tell me that you wont get a dead short from water? and it doesn't have to be 48 amps, as the circuit itself would already have a load on it that is at near full capacity.
What do you think we relied on before RCD's?

You crazy UK leco's should brush up on both your practicle and theory.

A bit of damp from tap water does not create a dead short, no.
 
are you trying to tell me that you wont get a dead short from water?

Yes. Plain water is not very conductive, specific conductivity of tap water is in the order of 10mS/m at room temperature. If the device remains energised, especially with DC, the conductivity will increase with the concentration of metal ions or TDS due to electrolysis of the metal parts.

For what it's worth, certain high-power electronic devices using water cooling actually place the water in contact with energised parts, but the water is kept pure enough to achieve a conductivity of just a few μS/m so that over a long insulated tubing path it is effectively an insulator.

What do you think we relied on before RCD's?

Earthing. The water in the fitting would have gently heated and fizzed and boiled itself off, leaving a working fitting but possibly with impaired IR due to a film of salts deposited on the surface and/or metal tracking.
 
Hold on a minute, are you trying to tell me that you wont get a dead short from water? and it doesn't have to be 48 amps, as the circuit itself would already have a load on it that is at near full capacity.
What do you think we relied on before RCD's?

You crazy UK leco's should brush up on both your practicle and theory.
Ermm... a dead short is a path of low resistance allowing a high current flow.
It has been suggested and most likely, that the water spray did not produce a low enough resistance to allow enough current to pass to trigger the fault current device. But rather, as in this case, enough of a leakage to earth to create an imbalance and thus trip the rcd.

The washing machine is unlikely to be much higher than 10-12 amps at full load so only a 1/4 of the fault current required to trip the mcb under fault conditions. Its unlikely that the fault leakage path created by the water would have sufficiently low enough resistance to achieve the required fault current to trip the mcb

So in the case of the OP scenario it was indeed an earth leakage fault.
 
On the evidence I've seen, Lucien's electrical theory knowledge is way ahead of you kid.
Apparently not.

Plain water is not very conductive
Throw a hairdryer in the bathtub and see how conductive it is.

If the device remains energised, especially with DC

When did DC come in to it? you can't change the story to suit your theory.

The water in the fitting would have gently heated and fizzed and boiled itself off, leaving a working fitting

You have a nice way with words.... the only one you left out was "gently massage" :D

Its unlikely that the fault leakage path created by the water would have sufficiently low enough resistance to achieve the required fault current to trip the mcb
Facts don't work on something being unlikely, but it was worth a shot :D

OP: It would be best to get the circuit and the machine tested for insulation resistance before powering back up, to avoid possible nuisance tripping or further damage. If the machine's guts are soaked, aside from RCD tripping, permanent damage to the programmer or motor controller / inverter may be caused by trying to operate it while they are still wet.
Why? apparently "
The water in the fitting would have gently heated and fizzed and boiled itself off, leaving a working fitting"
Source URL: UK - RCD vs MCB trip - https://www.electriciansforums.net/threads/rcd-vs-mcb-trip.179693/page-2#post-1583545
:D
 
Kidsolo - your response is poor and juvenile. I advise you to read some of Lucien's posts on other threads on this forum - you will find his level of technical knowledge very impressive, and also his attitude much more commendable than yours.

Stay on the forum though - you may well still be able to prove your worth if you try.
 
At my work place, the RCBO had tripped on some outdoor LED battens. They had failed, and slowly filled up with rainwater, and eventually tripped it. Think it tripped, as the rainwater had nowhere else to go. ?
 
I tried that hairdryer and bath thing but all I got was a small crack in the casing of the hairdryer. It still doesn't seem very conductive. Should I put some water in the bath and try again? Maybe try throwing the washing machine in as well for good measure? :)

BTW I'm out... I've got customers here!
 
Water is a very poor conductor, it's the deposits such as minerals which will increase its conductivity.
 
Facts don't work on something being unlikely, but it was worth a shot :D
Then present some yourself.
The Op asked why the rcd had tripped and not the mcb. We have successfully answered the question.
The reason I used the word "unlikely" is because in this scenario it was unlikely. I never said impossible. After all it's down to Ohms law and the characteristics of the protection device which determines the trip thresholds. The fact is that there was an imbalance detected before a short circuit developed, it was the rcd that had tripped.
[automerge]1571920786[/automerge]
Water is a very poor conductor, it's the deposits such as minerals which will increase its conductivity.
Yes, and its conductivity depends on the type and amount of impurities it contains. Sea water for example is far more conductive than tap water.
 
Had a similar fault the other day with a microwave oven tripping the 30mA RCD on my kitchen ring. My 15yr old daughter had placed a bowl of boiling water into the microwave, to cook some pasta, which had then overflowed and collected around the bottom, shorting out the motor that spins the glass plate around. I had to give my daughter a severe reprimand, drain all the water out of microwave and leave it in the airing cupboard to dry out for 24hrs. It's worked no problem after that. I tested the RCD afterwards and found out that it trips at 21mA, far less than the 160A required to trip the circuit breaker. Hence why my circuit breaker didn't operate either.
 
because a RCD reacts faster than a breaker. I said that in my very first post.
You can't say for sure that if there wasn't a RCD that the breaker wouldn't trip.
Ermm... No, not always, depends on the type & characteristics of the fault. (my bold)

I can't recall stating that the mcb would never trip, again this depends on the characteristics of the fault. If there is insufficient fault or overload current to achieve the trip threshold characteristics of the protection device then it will not trip.

Lucien Nunes has explained all this, you have yet to show any evidence to back up your claim that Lucien is wrong.
 
This is the way i have always understood it, and experience appears to support.

On a L-E fault, RCD will always trip first, it has to cos its got a 30mA limit and a 40mS time to hit, i dont think you can buy a MCB that would trip faster.
On a L-N fault , MCB always trips first, RCD sits happy
On a N-E fault, MCB never trips, RCD can and thats when you start chasing your tail finding the blessed fault, lol
 
I'm glad the OP got the question answered. re the difference between MCB and RCD. Thread slightly wandered off at a tangent for a bit though.

On a side note... PLEASE don't throw a plugged in hairdryer into a bathtub of water to see how conductive it is. :bathtub::electricplug:⚡:skull:
 

Reply to RCD vs MCB trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
566
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
717
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock