Evening everybody,
I’m wondering if someone wouldn’t mind answering a question for me about RCDs.

I had a water pipe burst behind my washing machine this evening, and once I’d isolated the leak I noticed the sockets had tripped. When I went to reset the breaker, I noticed that it was the RCD that had tripped, and not the MCB for the Ring Final Circuit which the washing machine is plugged into.
My question is ; why would the RCD trip but not the MCB? I understand that the MCB is there to protect the cabling in the event of fault current/overload, and that the purpose of an RCD is to interrupt the supply to reduce the effects of an electric shock. Would the RCD have tripped due to an earth fault such as the casing of the washing machine becoming live or water entering the socket behind the machine?
Thanks in advance and apologies for the lengthy post.

Regards
 
Yes, water has got in somewhere and created leakage path(s) to earth. Plain water is conductive enough that a wet fitting could have sufficient earth leakage for the RCD to detect. However, to trip the MCB would require a leakage path in the order of 500 - 1000 times lower resistance, which probably would not occur even with a socket outlet submerged in water.
 
with two units in a series arrangemant the fastest one trips first,
once that has tripped then there is no reason for the second one to trip
so it's purely a speed issue.
No it's a case if the water not producing a low enough resistance for fault current to flow, enough to trip the circuit breaker.
 
with two units in a series arrangemant the fastest one trips first,
once that has tripped then there is no reason for the second one to trip
so it's purely a speed issue.
Sorry dmx gotta disagree. They are 2 different devices offering 2 different functions. RCD provides earth leakage protection and a MCB overcurrent protection (Whether overload or short circuit).
 
Yes, water has got in somewhere and created leakage path(s) to earth. Plain water is conductive enough that a wet fitting could have sufficient earth leakage for the RCD to detect. However, to trip the MCB would require a leakage path in the order of 500 - 1000 times lower resistance, which probably would not occur even with a socket outlet submerged in water.
Thanks Lucien, will it be okay to leave the appliance/ socket to dry for 24hrs and the plug back in and try using it?
 
No it's a case if the water not producing a low enough resistance for fault current to flow, enough to trip the circuit breaker.

Woah, not so fast my friend. There is water involved, so there is going to be an earth fault. The reason the RCD trips first is because it is designed to trip within 40ms of a fault occurring.... way faster than any breaker or fuse will ever respond.
 
NO, A MCB will trip with an earth fault, but not when it is also protected by a RCD as the RCD trips too fast.
An mcb will require a much higher earth fault current to operate than an RCD. An RCD will only require a fault current of milliamps to operate whereas and mcb will require tens of amps over it's rated current, a current a 'wet' fault is unlikely to generate. However, yes, RCD trip times are faster than mcb times unless very high fault currents are involved.
 
Thanks for the responses guys. I understand that once the RCD had tripped the MCB wouldn’t trip, however what is the theory behind the RCD tripping? Would it be that the water had shorted between L-E due to its high conductivity?
 
NO, A MCB will trip with an earth fault, but not when it is also protected by a RCD as the RCD trips too fast.
An mcb operates in 2 ways, thermal overload and high current short circuit.
If the earth leakage path resistance is to high then then there will be insufficient current to trip the short circuit mechanism of the mcb. The mcb will only trip if the earth leakage current is high enough to operate the short circuit mechanism. Or if the thermal mechanism experiences a high enough excessive current flowing for a long enough period of time (depending on the type and rating).
A rcd however is designed to monitor current imbalances between L & N, so a much lower resistance earth leakage path will be enough to create a detectable imbalance (sensitivity depends on the rating of the rcd) to operate this device.
So in the op's scenario the small earth leakage caused by the water created a low enough resistance path for there to be a detectable imbalance for the in service rcd to operate first. If there had have been a "short circuit" then the mcb could quite possibly operate before the rcd.
 
Last edited:
In the case of short-circuit I don't think anyone is arguing specifically against that, but it's not relevant here as there wasn't a hard short. The socket outlet and the washing machine got sprayed with water, which is not conductive enough for a wet fitting to leak 46A (1.45 x 32) between a couple of small bits of brass and copper. The leakage probably ramped up slowly from nothing as the water penetrated.

OP: It would be best to get the circuit and the machine tested for insulation resistance before powering back up, to avoid possible nuisance tripping or further damage. If the machine's guts are soaked, aside from RCD tripping, permanent damage to the programmer or motor controller / inverter may be caused by trying to operate it while they are still wet. In a hurry, I would change the plug and socket, then test the machine.

so a much lower resistance earth leakage path will be enough to create a detectable imbalance
Source URL: UK - RCD vs MCB trip - https://www.electriciansforums.net/threads/rcd-vs-mcb-trip.179693/page-2

Your explanation is good, but I think you meant higher, not lower!
 
In the case of short-circuit I don't think anyone is arguing specifically against that, but it's not relevant here as there wasn't a hard short. The socket outlet and the washing machine got sprayed with water, which is not conductive enough for a wet fitting to leak 46A (1.45 x 32) between a couple of small bits of brass and copper. The leakage probably ramped up slowly from nothing as the water penetrated.

OP: It would be best to get the circuit and the machine tested for insulation resistance before powering back up, to avoid possible nuisance tripping or further damage. If the machine's guts are soaked, aside from RCD tripping, permanent damage to the programmer or motor controller / inverter may be caused by trying to operate it while they are still wet. In a hurry, I would change the plug and socket, then test the machine.



Your explanation is good, but I think you meant higher, not lower!
yes, it was a mistake, I tried to edit it but for some reason I couldn't. Thanks
 
It’s not a race RCD -V- MCB, the RCD is there to detect earth leakage current and will operate within 40mS if a leakage current ‘exceeding’ 30mA exists.
In the situation described it would appear that an earth leakage current has caused the RCD to operate.
A MCB May permit, for example 3-5 times the rated current to flow before it operates with a much longer permitted disconnection time (typ 0.4s [400mS] if TN-S.
A short circuit current will reduce this time but that doesn’t sound like the fault described.
 
Thanks everyone for your replies. I took the back off the washing machine and there didn’t seem to be a lot of water in there. I replaced the socket and plugged it in and all seems to be working fine :D

beeg
 

Reply to RCD vs MCB trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
542
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
995
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
652
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
720

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock