It's for circuits not requiring 30 mA protection.
 
You need to have a revise on the rules Concerning TT systems TBH toptrics, thats the best bet mate as you needed to ask, I promise I am not being nasty, but a refresh regarding it may be of benefit for you.

Mike
 
Morning.
What is the reason for having a 100ma rcd as a main switch on a tt system instead of 30ma

Why, ....because you have this numbty 200Ra ohm figure in BS7671 whichi s no good to man or beast, (certainly not for any protection purposes) and 30mA RCD's looking after several circuits on each side of the CU. The trouble is RCD's are NOT the most reliable protection devices out there, so if one of those normal RCD's fail to operate under fault conditions etc, you have a reasonable back up in a 100mA S type RCD up-front device....
 
There is an interesting article in jan PE mag on this...and it argues that a 100ma S type will fall foul of reg 531.2.9 re- ensuring downstream devices tripping before upstream in the event of a fault. The conclusion was a minimum of 300ma S type would be required for final circuits with 30ma protection.
 
Doesnt make sense, 100ma wont meet the disconnection times for final circuit, also wouldnt 30ma trip before 100ma so why would it need to be s type.
 
Doesnt make sense, 100ma wont meet the disconnection times for final circuit, also wouldnt 30ma trip before 100ma so why would it need to be s type.

Of course it will. It will give you a max Zs of 500 ohms per circuit protected by it. A 30 mA will trip before a 100 mA but what if you get a higher leakage current of say 100 mA you need to then delay the 100 mA.
 
The 30 ma rcd won't see the fault as it will not be protecting the circuits that the 100 ma rcd is protecting. The main this is all circuits on a tt have to be protected by an rcd, does this make it any clearer.
Ben
 

Reply to rcd in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock