Discuss Rcd100ma or 80a in the UK Electrical Forum area at ElectriciansForums.net
Iona222
Trainee
Whats the maximum breakers current you should put on one. Would you go to 140amp on a 100amp during to diversity. Its there a rule of thumb.
Cheers gents.
Sorry - not sure I’m understanding the question. Are you asking if it’s OK to have a single RCD rated at 80A upstream of say 5 x 32A MCB’s?
Sorry mate poor description. OK say your in front of a consumer unit and there isn't ant rcd protection. So being a quality sparky like myself you decide to fit one.
So you get say a 100amp rcd, how much amps should you put for it to cover. Like 32amp 32amp 32amp, 40amp, 40amp, 6 amp 6amp. Total 180 amp
What the total. Cheers.
It’s supposed to be no larger than the rated amperage on the main switch….seems impossible when you can have @ least 4-5 32amp mcbs before anything else.
Diversity may not be appropriate @ that point but on the final circuits it can be used.
Personally I wouldn’t worry about it,using an amp meter on the install would show low current use anyway on Flc.
The RCD should be protected against overload either upstream or downstream. Examples:
100A RCD, 100A supply: total of MCB ratings not important because RCD protected upstream.
63A RCD, 100A supply: total of MCB ratings must not exceed 63A so that RCD is protected downstream.
63A RCD, 100A supply, total of MCB ratings with non fixed loads: No good, RCD is not protected.
You will often have a situation where due to diversity, the demand (and hence the main fuse rating) can be much lower than the total of the MCB ratings, but the RCD rating must be sufficient to handle the In, not the demand.
Have a re-read of chapter 13, may help clarify your thinking
Reply to Rcd100ma or 80a in the UK Electrical Forum area at ElectriciansForums.net
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
I'm trying to find a way of energy logging a home to help plan a battery installation. Ideally tracking import by hour and displaying some...
Hello. So, I would like to know how I can choose the correct circuit breaker value when doing a new installation. My example is: I have 16...
I’m planning on putting in a small (10x10) detached shed for garden storage plus a freezer for meat storage, an in-wall AC unit (for temperature...