On a caravan site, just tested the main incoming Ze and PFC.

Ze= 8.67Ohms, (TT System, so less than 21Ohms OK)

but PFC was 21AMPS??? as in 0.021kA

there are RCD's at different points throughout the installation, which keep tripping randomly.

also switching the shower lights on, was tripping the RCD for the Cafe (both on different DB's, only fed from same DB at origin but different ways)

Any thoughts or comments... I need some HELP?!
 
thanks for the quick response...

they are seperate buildings but next to each other.

and no shared earths, or borrowed neutrals... though thats only from a visual inspection, doing a periodic tommorow. they seem to all be back to relevant earth / neutral bars in the CU, and then obviously through the supplies back to incoming DB.
 
yeah i'm going to take another one with me tommorow. But considering he's having problems with tripping RCD's, i'm not presuming anything, whether it be a faulty tester, or purely a problem with the circuit, especially neutral/ earth arrangments.
 

Reply to REALLY Low reading PFC Test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I’m currently doing some testing on some site temps I have a three phase trip system the tails from the head go into a 100 amp RCD which feeds a...
Replies
8
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
912
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock