Tuttle

-
Arms
Reaction score
74
Amendment 1 added a "Reference Method" column to the schedule of test results and while this makes perfect sense for new installs I am a little confused about what should be entered into this column for consumer unit changes, i.e. where you can't see all the cable runs so can't be sure what the reference method for each circuit actually is. Do you enter what you have assumed the reference method to be, perhaps with an additional note somewhere to say that it hasn't been verified, or enter n/v or n/a or something else? What's everyone else doing?

I've got my Part P assessment coming up soon and I'm planning on showing a job that includes a CU change so I'd like to get this right.
 
You are only certifying your work, so you would put N/A in this column unless you can the whole length of the run and its installation method. Or if you had installed a new circuit then you would put the relevant one ion for any you have done.
 
Amendment 1 added a "Reference Method" column to the schedule of test results and while this makes perfect sense for new installs I am a little confused about what should be entered into this column for consumer unit changes, i.e. where you can't see all the cable runs so can't be sure what the reference method for each circuit actually is. Do you enter what you have assumed the reference method to be, perhaps with an additional note somewhere to say that it hasn't been verified, or enter n/v or n/a or something else? What's everyone else doing?

I've got my Part P assessment coming up soon and I'm planning on showing a job that includes a CU change so I'd like to get this right.

You wont get beaten up for either putting the incorrect ref method in or not putting one in at all.
 

Reply to Reference Method - Schedule of Test Results - CU change in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock