Looking at some work for a lady who has recently had a new fitted kitchen.
She was concerned about some bits so I had a quick look and found a 3.5KW oven on 1.5mm T&E to a 13A plug top.
Can anyone tell me the reg numbers for loads over 3KW needing thier own circuit, not using T&E into a plug top and for following manufacturers instuctions (and any others that may be wrong).
Thank you.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

Richard Burns

-
Mentor
Arms
Esteemed
Cooking loads over 2kW should not be supplied from a ring according to a note in appendix 15, T&E is advised in the ISITEE guidelines as being unsuitable for a use in a plug becauce the cable is not designed for frequent movement. 134.1.1 and 510.3 "shall take account of manufacturers instructions".
Cable is suitable for the load.
 
Not to mention twin and earth into a plug top is proper badgers....

I have seen an entire brand new block of flats where all the fitted ovens were installed by the kitchen company on 1mm twin and earth via a plug top into a 13a socket directly behind the oven (no isolation switch) fed from a 40a radial in the board

Nice work fellas
 

Doomed

-
Arms
  • Thread Starter Thread Starter
  • #4
Cooking loads over 2kW should not be supplied from a ring according to a note in appendix 15, T&E is advised in the ISITEE guidelines as being unsuitable for a use in a plug becauce the cable is not designed for frequent movement. 134.1.1 and 510.3 "shall take account of manufacturers instructions".
Cable is suitable for the load.
Thank you
 

telectrix

-
Mentor
Arms
Esteemed
what reg. pertains to installation practice that is shite? we don't need a reg. to see this.
 

littlespark

-
Arms
Esteemed
Advent Win
kitchen fitter needs to pay to have it done again.
was it a joiner, or a Big Shed installation team?

I bet it was Wren
 
Not to mention twin and earth into a plug top is proper badgers....

I have seen an entire brand new block of flats where all the fitted ovens were installed by the kitchen company on 1mm twin and earth via a plug top into a 13a socket directly behind the oven (no isolation switch) fed from a 40a radial in the board

Nice work fellas
They are plugs NOT plug tops which are the covers for the plugs.
 
Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Regs book at office in the Electrical Forum area at ElectriciansForums.net

Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom