There is also a distinction between the "Is this safe?" sort of question for EICR coding and "Is this acceptable design practice?" where you are planning on a system and (at least hopefully!) that is a higher standard to be met.

So in this case if you found the cable protected by the sum-of-MCB being within range it is clearly not going to overload and so is safe. But equally if you were desiging it and following best practice you would aim for your cable protection to be at the feed end of the cable if at all possible, as not only do you guarantee overload protection but it is likely going to be a better match for fault/short protection as well given the likely end of cable Zs range.
 