Good morning all,

Apologies if you have gone over this a number of times before (I have tried searching for a thread, and have found some that have touched on what I'm after but not quite explicitly enough).

If the measured PFC is greater than 6ka (for example) with circuit-breakers' breaking capacity of 6kA, I need to check the breaking capacity of the fuse supplying the board.

How do I work out if the rating of the service fuse makes it acceptable?

Is it as simple as just making sure the capacity of the service fuse > the measured PFC ?

Which is how I read 434.5.1 "...the rated short circuit breaking capacity of each device shall be not less than the maximum protective fault current at the point at which the device is installed.

"A lower breaking capacity is permitted if another protective device or devices having the necessary rated short-circuit breaking capacity is installed on the supply side."

Or do you need to check the relationship between, how long the service fuse would take to blow at 6kA (ok fraction of a second) or do you need to prove the fuse would blow before reaching 6kA even in a dead-short situation?

And if so, where in BS7671 is the information I'm looking for/ how do I work it out?

Thanks, Chris
 

Reply to Relationship between Cut-Out Fuse & MCB PSCC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
606
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock