Afternoon All,

Maybe an odd question. For the last 8 years I've been in this industry I have always fitted single and 3 phase disboard/CU's with locks and no remote isolator other than on a locked main panel.

I'm on a new job where we are using a mix of Siemens 3 phase boards and Crabtree single phase boards, all of which have a sticker inside them.

"TO COMPLY WITH BS7671 All consumer units that are intended to be locked after installation must be supplied via a separate means of isolation fitted adjacent to the unit"

Anyone able to shed any light on this? Is it correct? What regulation states this?

A lot of these boards will be accessible to students. You can only imagine the havoc students would cause with a fully accessible isolator. o_O

BS7671 Remote Isolator.jpg
 
Contact Electrium technical and ask which regulation they refer to. Don't have the time to look it up but my first thoughts would go to emergency switching ?
 
This looks like the beginning of another great myth which will soon be turning up on EICRs everywhere.

You can almost see the future on this one, hundreds of DBs with cheap isolators retrofitted to them with dodgy crimp connections to extend the feeds and contacts burning out all over the shop.
 
Only thing I can find is this: but it's stating that the isolator should be locked away..

upload_2018-11-19_13-21-33.png
 
EDITED..... Ignore... Should have looked at 17th Ed.
 
Dangers come in a variety of known and as yet unkown forms.
Presumably it's written vaguely to cover any current or future eventuallity.
RCBO protection may not be on all circuits in all installations.

For example in Student accomodation,
A Brown (or Black or Grey) cable hanging out of a light fitting in a corridor with the end of the cable showing copper.
Does that present a Danger?
 
Last edited:
Dangers come in a variety of known and as yet unkown forms.
Presumably it's written vaguely to cover any current or future eventuallity.
RCBO protection may not be on all circuits in all installations.

For example in Student accomodation,
A Brown (or Black or Grey) cable hanging out of a light fitting in a corridor with the end of the cable showing copper.
Does that present a Danger?


Brown, black and grey cables are all line colours so should be treated as such unless marked otherwise.

Having previously had a nasty belt from neutral to earth I'd also argue a blue cable would present a danger.

I still don't see how an external isolator would help?

What happens in more public areas where boards are locked in cupboards? Do we start fitting emergency stops everywhere with contactors on the supply to the board?
 
Dangers come in a variety of known and as yet unkown forms.
Presumably it's written vaguely to cover any current or future eventuallity.
RCBO protection may not be on all circuits in all installations.

For example in Student accomodation,
A Brown (or Black or Grey) cable hanging out of a light fitting in a corridor with the end of the cable showing copper.
Does that present a Danger?

Yes that presents a danger, or should at least be assumed to present a danger until proved otherwise.
But what is your point? Are you saying that there should be an accessible isolator adjacent to a locked DB in case this situation occurs?
 
It seems fair enough to identify the CU isolator as an emergency device. For example a room contains smoke and a smell of burning with no obvious source. What's the first-line response?
 
It seems fair enough to identify the CU isolator as an emergency device. For example a room contains smoke and a smell of burning with no obvious source. What's the first-line response?

So what happens in public buildings where boards are fitted in locked risers and store rooms? Do we put emergency stops in? Rotary isolators outside the doors?
 
Activate the fire alarm and get out?

Good advice, I don't have a fire alarm in my house but I do have an extinguisher and would prefer to stop the house burning down if I could do it safely. I'd be a bit miffed if my friendly electrician had locked down the CU and wandered off.
 
Good advice, I don't have a fire alarm in my house but I do have an extinguisher and would prefer to stop the house burning down if I could do it safely. I'd be a bit miffed if my friendly electrician had locked down the CU and wandered off.

Why would you have a lockable CU in a house?
This thread is obviously concerned with non-domestic installations where lockable DBs are quite common, so why drag it off track with domestic nonsense?
 
But the OP hasn't stated where these CU's will be mounted and what the building is. Just that students can get to the CU's.
Nothing wrong with locking CU's. All depends on the circumstance.
 

Reply to Remote Isolator On Locked Disboard/CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I went along this morning to quote for an EVCP install. I thought it was a domestic house but it was a B@B. It has a 3 phase supply. I always...
Replies
49
Views
10K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock