Hi fellas. Looking at an old domestic MK board with BS 3871 CBs. Standard arrangement, E&B all good, TNCS. Issue is there is no 30mA protection but all circuits are fed from a 100mA BS 4293 RCCB which also acts as main switch. Not sure why unless previous TT and converted...? Problem is this fails test at 100% rated trip current. Does anyone know of a device I can use as a straight replacement or am I probably looking at updating the board if they will go for it?

cheers
 
if the existing RCD is a delay type, don't think most MFTs will tewst it. if it is, bung it in an enclosure upfront and fit 30mA RCD as CU main switch.
 
Cheers. It's not an 'S' type device. Not sure i'm happy with covering all 7 circuits with a single 30mA RCD plus the work i'm being asked to do carries no requirement to install additional protection. I could realistically just carry out the work and note the deficient device on the cert as it still fulfills it's role as a main isolator and there is no requirement for 100mA protection on this installation, perhaps issue them a potentially dangerous condition report too. Want to do the best for them though so will try to convince them to let me correct it. Best is obviously a new board and bring it all up to standard if they will swallow it in a triple dip recession....!
 

Reply to Replacement for BS 4293 RCCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
Hi all I am in an industrial unit and the 100mA RCCB keeps tripping. They use it as the main switch inside of the unit's distribution board. The...
Replies
41
Views
6K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Customer has a large metal caravan with three phase supply feeding 3 metal Consumer units with split load RCD outlets contained within - all...
Replies
18
Views
2K
Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock