SeanA

-
Reaction score
4
A friend of mine is German and is used to using E27 light fittings rather than the standard Bayonet B22 fittings that are used in the United Kingdom she uses an adapter to convert B22 to E27 for her fixed ceiling lights as very few installations in the United Kingdom have E27.

She has asked me if it's possible to replace the B22 fittings with E27 fittings. I have managed to get some E27 fittings from a large well known DIY store (E27 fittings can be quite hard to get) and I plan to install them. I was wondering however if there was anything I needed to know before installing? I am aware that unlike Bayonet fittings it does matter which way it's wired up as the screw holder is neutral and the center pin is live.
 
If all you’re doing is changing the b22 lamp holder on a pendant to a e27, then you’re right, live to centre pin, neutral to the outer screw.

a lot of UK decorative fittings come with e27 lamp holders anyway, so it’s not unusual.
 
In Europe ES lamp holders should comply to en60238 and have no polarity bias. Manufactured to this srandard it should be irrelevant where you connect the live conductor.
 
as above. it's always been convention to connect L to centre contact, but mre recent fittings are manufactured so that it soesn't matter. however us old farts still connect L to centre. i might change when i run out of red/black cable.
 

Reply to Replacing bayonet fittings with E27 fittings (UK). in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I live in Australia; you can use a socket tester to test the RCD for the power outlet circuit. Plug device to a 3-pin wall socket, set testing mA...
Replies
2
Views
848
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all Is anyone aware of the change to solar generation FIT payment contracts for existing installations. (FIT payment scheme closed in 2019)...
Replies
8
Views
816
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
979

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock