Tomorrow I’m changing my consumer unit in preparation for my NICEIC assessment on 13th November and have a few queries.
Firstly, current cu only has 4 circuits sockets up & down and lights up & down, so hopefully a pretty straight forward swap.
I can unplug 95% of loads on both ring finals, except for the oven and the boiler, both of which have LCD/LED displays. So when it comes to doing the insulation resistance test, would the 500v dc test damage either of these appliances LCD’s or LED’s? The oven and hob ignitor are connected behind the kitchen units.
Also, upstairs we have GU10 spot lights on the landing and bathroom, can’t remove them to do the R1+R2 test as they’re very tight and as we only rent, I can’t cause any damage to the ceiling. So would it be ok to just do the R1+R2 on the final light fitting in the rear bedroom or should I try to find the spots wiring in the loft?
If they have isolators, turn them off and run the full suite of tests (L-N, L-E and N-E). If they don't have isolators join L+N at the board and test L+N to E. This is acceptable when making alterations to existing installations. You just put a LIM in the live-live column for IR.
Can you access the loft? If so, do the tests from above. It's nice to verify CPC continuity through out, so at the very minimum I would check R2 at each location using a wander lead.
Unfortunately neither appliance has an isolator, but thanks for the L+N to E tip.
I have access to the loft, but not boarded out, so will have to be extra careful up there.
if you only have 4 circuits, i'd fit a BG 6 way RCBO board with 4 RCBOs .get gear from TLC the BG compact RCBOs are ony £15.60 inc. vat each.
I’ve already bought an MK 12 module board, which leaves 4 modules for future additions.
A couple of anomilies here
1. IMO its not your responsibility to change the CU. If I was the Landlord I'd be hopping as its unlikely to be part of your initial contract. However, if the landord has given prior permission to upgrade his/her property then fire away. as you will have to use his/her name on the cert.
2. Fixed heating appliances should have local isolation and if connected to a RFC should be by plug and socket or possibly by SFCU/FCU.
Reply to Replacing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...