Am currently pondering the following situation:

- Single phase PVC board, domestic, in an area where TN-C-S is the norm (underground supply etc).

- Most circuits protected by 30mA RCD, except lights (B6 60898 MCBs).

- Pre-checks before simple job (on garage circuit) reveal no earthing conductor (10mm bonding to gas, 6mm bonding to water with loose clamp - upgraded to 10mm with new clamp while I was there)

- Zs @ DB = 27.1Ω

- Happysteve notes lots of shiny metal light switches, and rather old looking metal light fittings. Board looks like a 1990's DIY special (the BS951 clamp on the end of the SWA supplying the garage, for instance).

- Have chat with customer about necessity of having an earth, explain WPD will charge for this, they are happy to get WPD to provide one. Phone WPD on behalf of customer, get the ball rolling.

- As a temporary measure, to provide shock (and fault) protection, move 2x lighting circuits to 1x B6 on RCD-protected side of board.

- All circuits now protected by 1x 30mA RCD (same as having an RCD main switch).

Question is, when I go back to the job (to do the actual "simple job") after WPD supply a reliable earth, do I move the lighting circuits back to the non-RCD side of the board? Would not comply with current regs on at least 2, possibly 3 counts (cables buried in wall, domestic lighting circuit, possibly bathroom but haven't checked for supplementary bonding)* but on the other hand would be no worse off than before I made the "distress change". Board is Steeple - not sure on availability of RCBOs (and probably wouldn't fit anyway), could put the lighting circuits on a couple of RCD spurs I guess.

Think of it this way: if earthing/bonding had been in place, and I'd been working on a circuit other than a lighting circuit, I would have left them alone; and the only reason I moved them was I couldn't in good faith have left it like that, given the very real shock risk due to the presence of a single fault on an installation that didn't give me confidence it was installed professionally.

Any thoughts? I'm not going to lose any sleep over this, and I'll probably have a couple of weeks to mull it over! :)

* Edit: clearly 3 counts, even if there was supplementary bonding. Head was in "EICR mode", sorry!
 
I'd leave it as you've put it, using RCD. Remember, it's not a double RCD board so no need for separate lighting up and down (although preferable). With the state of the existing installation I'd be thinking RCD is better than not.
 
here perhaps. and loads of other listings. buy one, test it, fit it.
 

Reply to Restoring circuits after temporary "distress change" in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
317
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
726
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
473
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock