Discuss Retrospective Application of the 17th Edition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

Shakey

Hi gents, so someone has finally asked it - well i have to fit rcd's/RCBO's to existing circuits when the 17th kicks in???

Well here is my view:

There is one ENORMOUS change in the 17th which has been largely overlooked

The Schedule of Inspections in the model forms appendix has been ammeneded to include the new requirements, so all the things we discuss (cables buried 50mm deep/earthed metallic protection/ 30mA RCD etc) are now check boxes on the new form

Now look at the bottom of the form

They tell you, you can tick to say inspected and satisafactory, or X to say unsatisfactory (plus the usual N/A and LIM)

Now look at the little comment next to the X : it says

APPLICABLE TO PERIODIC INSPECTIONS ONLY:eek::eek:

think about it

yes that's exactly what it means

it means you CANT inspect something when doing an EIC and say it is unsatisfactory!!!!!

So lets say you get asked to put a new shower circuit in. you would have to RCD it. but your inspections would by default include any wiring you come accross as you ar e pulling through, and would include the CU you start at, and the bathroom circuits you finish at. And everything along the way would have to be ticked to say 'satisfactory'. Because any cable you see that is NOT 50mm deep on an RCD, unless its got earthed metallic protection would be an X

And you cant X something unless its a PIR!!!

Got a feeling this could blow up a bit towards the end of the year

what do you guys reckon????:rolleyes:
 

Reply to Retrospective Application of the 17th Edition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Experienced Electrician, C&G 236 Parts 1 & 2, AM 1 & 2 18th Edition Am 2. (JIB Gold Card) I've been out of the trade for some time, but did a...
Replies
2
Views
835
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi guys I have been tasked with upgrading some old rewireable fuseboards for a food warehouse that runs continually 24/7. I was asked to do an...
Replies
10
Views
2K
Am I on the right lines, I ask? I've just recently moved into this house which is nicely equipped with a large 15 circuit CU unit with a split...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock