Good evening all !

I've been reviewing test sheets lately off sub contracting electricians not in a official capacity as of yet and there are a few items I have noted but would like peoples thoughts.

1. Cooker wired in 6.0 T+E Ref method 101 32a Rcbo surely a Code 2 but no mention in test sheet what would you recommend

2. Upgrading of gas and water bond in an old wylex consumer unit would this require an installation cert ? Plus on same job changing of a light to a different type in a special location would this be part p or classed as maintenance ?

Thanks all
 
Good evening all !

I've been reviewing test sheets lately off sub contracting electricians not in a official capacity as of yet and there are a few items I have noted but would like peoples thoughts.

1. Cooker wired in 6.0 T+E Ref method 101 32a Rcbo surely a Code 2 but no mention in test sheet what would you recommend Care to expalin futhere Is this a EICR or a EIC.

2. Upgrading of gas and water bond in an old wylex consumer unit would this require an installation cert ? Plus on same job changing of a light to a different type in a special location would this be part p or classed as maintenancne? Like for like replacement so no need for part p notification.

Thanks all
......
 
It's on EICR how can upgrading of bonding be like for like surely you have to test each circuit to confirm zs readings etc ...?

Why would you need to test every circuit when installing main bonding? Just install it and test the connection then go to pub haha
 
6mm ref. method 101 = 27A. OK, the 32A MCB is over rated for overload , but as the cooker has a fixed max. load which will be <27A unless it's a beast, then you might consider that overload protection can be omitted (433.3.1 (ii))
 

Reply to Reviewing test sheets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock