Looking for some advice, I have tested a property and on the ring main circuits the values do not tally up using the formula

(r1 + r2) / 4 = R1+R2

Although the R1+R2 tallys up using the formula

R1+R2 = Zs - Ze



Is this an actual fault that needs recording on a periodic ? I have been told it is but i cant find a regs number to go with it


Thanks
 
The calculation method (2) cannot be relied upon to be accurate, however it is an acceptable method when doing PIR's in certain circumstances. I have done this before out of curiosity and the results and calculations i got were almost the same.

On a new installation, the measured value should be recorded as technically, the installation should not be energised until dead testing is done.

So, in other words, test it, dont calculate it if possible.
 
Looking for some advice, I have tested a property and on the ring main circuits the values do not tally up using the formula

(r1 + r2) / 4 = R1+R2

Although the R1+R2 tallys up using the formula

R1+R2 = Zs - Ze



Is this an actual fault that needs recording on a periodic ? I have been told it is but i cant find a regs number to go with it


Thanks

the whole idea of the ring final circuit continuity test is to find any problems with the ring ie is it a ring or are there interconnections which make it appear to be a ring on the end to end tests,if the readings are bit out on one or two s/o it could be a simple loose connection, (these wont show on the end to end if the conductors are twisted at the s/o) or if you are measuring at the tubes simply worn socket outlets, I did a test last weak where the R1 R2 readings were completely different on the two sides of a twin socket,the s/o being defective internally, if your Zs readings at each socket are much the same without any significant increases or decreases around the circuit then I wouldnt worry, if they all over the place then coupled with the continuity readings i would dig a bit deeper

The regs only quote atest is required 612.2.2, GN3 gives more specific guidance, any problem should be marked on your pir as requires further investigation
 
Last edited by a moderator:
I agree with trebor,

The purpose of the test is to find faults !!!!!!!

The equation R1+R2 = Zs - Ze MUST NEVER BE USED

2 words PARALLEL PATHS... parallel paths = false readings. I cant believe anybody would even think of using that equation.

1 possible reason for your readings not matching may be due to the size of the cpc. older circuits incorporate 2.5/1 and therefore 1.67 would not apply !
 

Reply to Ring Circuit Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock