Discuss Ring end to end results not text book for cu change.. do we need to ensure 1.67 times in the UK Electrical Forum area at ElectriciansForums.net

bleach

-
Reaction score
0
Hi,

Cu change pre tests (TT) indicate non text book results: r1=072, rn=0.92, r2=1.58 another ring: r1=0.67 n=0.67 r2=1.60

As can be seen the r2 values are more than 1.67 times r1 or rn possibly due to loose connections. Are we responsible to try and bring these values in line for a cu change only? or just record?

Many thanks people
 
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

Even so, r1 should be about the same as rn. The r2 figure does look high. I too would suspect loose connection either in one (or many) sockets or a hidden underfloor JB:thumbs_down:
 
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

Hi,

Cu change pre tests (TT) indicate non text book results: r1=072, rn=0.92, r2=1.58 another ring: r1=0.67 n=0.67 r2=1.60

As can be seen the r2 values are more than 1.67 times r1 or rn possibly due to loose connections. Are we responsible to try and bring these values in line for a cu change only? or just record?

Many thanks people

The second set of results look spot on for a ring with a 1mm CPC, so as long as Zs requirements are met then it's fine. (i.e r1(0.67)x2.5=1.67))

The first set of results are a bit out. Assuming the r1 is correct then the rn is a bit high, as Taylor said a loose connection somewhere perhaps.

As for the responsibilty, 'yes' I'm afraid. You would need to investigate as to why the resistance for the neutral is almost 30% greater than the r1. It's not just a case of testing the installation for the sake of writing the figures down, any faults found need to be rectified. I (now - didn't when I first started to my detriment!) always add in my quote that if any complications arise then their may be additional costs.
 
Last edited:
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

If you are doing a CU change then you are assessing whether the circuits you are reconnecting are safe to reconnect not whether they are complaint with the regulations, although this is a very good guideline to work to.

In your case I would be tempted to measure the resistance again and make sure your probes are in good contact with the cores to eliminate any contact resistance errors.
If the results are still out then you can either decide that they are not too far out and so you can safely reconnect them as the Zs would still be complaint or you can provide in your quote for the CU change the additional cost of investigating and resolving the higher resistance values.
 
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

I think r1 and rn should only have a difference of 0.05 ohms. That is the max acceptable difference in the measured values. That's what I got in my brain anyway!
 
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

The second set of results look spot on for a ring with a 1mm CPC, so as long as Zs requirements are met then it's fine. (i.e r1(0.67)x2.5=1.67))

The first set of results are a bit out. Assuming the r1 is correct then the rn is a bit high, as Taylor said a loose connection somewhere perhaps.

As for the responsibilty, 'yes' I'm afraid. You would need to investigate as to why the resistance for the neutral is almost 30% greater than the r1. It's not just a case of testing the installation for the sake of writing the figures down, any faults found need to be rectified. I (now - didn't when I first started to my detriment!) always add in my quote that if any complications arise then their may be additional costs.

Doesn't warrant the installation as unsafe in my eyes, and other than noting/mentioning, I see nothing wrong with reconnecting on a board change and there is no way I would consider it my "responsibility" to piddle about tightening all connections to bring rN down such a small amount. If it's miles out then fair enough, but 0.2 of an ohm?!

Also, I don't class that as a fault, and I don't see how you could even justify telling a customer that it is a fault that needs rectifying.
 
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

Doesn't warrant the installation as unsafe in my eyes, and other than noting/mentioning, I see nothing wrong with reconnecting on a board change and there is no way I would consider it my "responsibility" to piddle about tightening all connections to bring rN down such a small amount. If it's miles out then fair enough, but 0.2 of an ohm?!

Also, I don't class that as a fault, and I don't see how you could even justify telling a customer that it is a fault that needs rectifying.

Thats fair enough chap.

Perhaps I did word it a bit too strongly. I'd still spend 30mins tightening up a few sockets though and get the figure down a little.
 
Re: Ring end to end results not text book for cu change.. do we need to ensure 1.67 t

Thats fair enough chap.

Perhaps I did word it a bit too strongly. I'd still spend 30mins tightening up a few sockets though and get the figure down a little.

I tend to do that in my day job, but I'm paid a wage and it's completely irrelevant how long I spend on each job, they're also voids, but those figures aren't anything to hugely worry about and are something we continually come across. I just think that when it comes to charging for that work, it's a bit of a grey area because There's not enough discrepancy in the reading.

Bonding/earthing and IR issues are probably the only things I'd refuse a board upgrade over, anything else can just be left unconnected if the client objects, wrote it down, get a signature, and then they can do as they please.
 

Reply to Ring end to end results not text book for cu change.. do we need to ensure 1.67 times in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Initial fault was RCD tripping, narrowed down to a ring final cct. IR tests on that cct with all loads removed were showing almost zero between...
Replies
4
Views
1K
Hello, I have tried to search the forum but have not found anything although this must have been asked a thousand times. When completing a board...
Replies
17
Views
2K
Working with a spark, now when we change a CU no new circuits just old for new, We do all end to ends on rings, IR tests and Zs making sure all...
Replies
36
Views
3K
Been to quote for a job this morning, The house has 2 CU's one is eco7 for 5 storage heaters, the other was upgraded in 2009 and all wylex rcbo's...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock