Please could someone enlighten me on how grouping factors apply to ring final circuits run together, e.g. sharing holes through joists and walls, in a domestic situation?

For one RFC run in 2.5mm T&E under first floor boards (ref method B) the cable rating is 23A.

If you group two RFCs together, i.e. four 2.5mm T&E cables, then I think this counts as two circuits giving a grouping factor of 0.80 and therefore a cable rating of 18.4A, which is less than the allowed minimum of 20A for each leg of the ring.

This seems to suggest to me that you can't group a 32A 2.5mm T&E RFC with any other circuit?

What I really want to get to the bottom of is: is it ok to run two 32A 2.5mm T&E RFCs together, though the same joist holes, and if so how can this be justified?

Thanks
 
Another area where you need to use a bit of commonsense. Look at your question again, this time considering that it will be highly unlikely that either of these two ring circuits will be carrying it's full load capability (or anywhere near it).
 
Tuttle I've been doing this for more years than I care to mention and have to agree with E54 that in these type of situations we are always in danger of trying to "over engineer" things.

Yes your correct technically in some ways, but I have yet to see any problems caused by bunching cables through a joist in any domestic situation and you running 2 RFCs together, or any circuits together in a domestic situation is unlikely to cause any problems at all
 
Hate to think what the de-rating factors going to be where all the installations cables come together to drop down to the CU then!!! lol!!

As Malcolm has stated, don't over think these situations, the real loadings on a domestic installation is generally far lower than most think, or even calculate it will be....
 
as long as you don't need lubricant to pull cables through joists, i wouldn't worry about grouping factors. agree with previous posts by the other members of the old farts club.
 
Most CU's have all of their cables exiting together - does that mean that all the circuits need derating? I don't think so.
 
Theoretically and correctly, ...Yes!! But the grouping de-rating tables in BS7671 and OSG's are based on worst case scenario's, ...(eg, all circuits operating at it's full load capacity) which 9 times out of 10 or more, will not be the case!!
 
What happens when they add underfloor heating pipes and get the void nice and toasty. Your grouping factors fine but you could fry an egg on your cables!
 
That's not really your concern is it, you can't design and install an installation based on what might or might not happen in the future. (especially second guessing a plumbers installation) So long as You ideally keep all cable runs away from existing central heating pipework as far as is possible, then all should be fine...
 
Last edited by a moderator:
I seem to remember reading somewhere that the classic ring final (2.5 on 30A ) had all the factors taken into account (insulation, grouping, thermal,etc).
it kind of makes sense cos effectivly you got 5mm cable. 2x2.5mm equals 2x27Amp=54amp. so your only loading 3/5 of cable capacity.
lots of ISH-ness to be taken into account of coarse.
only ever seen overheating in old pub with about 20 circuits pulled tight in joist holes.... it did catch fire.
bit unlikely domestic.
 
Hate to think what the de-rating factors going to be where all the installations cables come together to drop down to the CU then!!! lol!!

As Malcolm has stated, don't over think these situations, the real loadings on a domestic installation is generally far lower than most think, or even calculate it will be....

I have found grouped cables running up from CU into a ceiling void are usually quite drafty and thus have a 'cooling' effect. With this in mind I tend to drop the Cg at this point and only ever consider grouping where cables are bunched together with cable ties.
However, each installation has its own problems and needs to be looked at on an individual basis
 

Reply to Ring final circuit grouping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
274
Hi, I've got a customer who wants a 10.5 kW shower installed in his bathroom. As it happens he already has two unused 4mm T&E cables run from the...
Replies
18
Views
2K
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
1K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
543

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock