Discuss Ring Final Circuit Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

AA410

Hi all hope you can help had a spur to fit on an old ring final circuit today that is made up of the old 3092 and old twin and earth were it has been extended in the past the readings i got end to end L 0.16 N 0.16 E 0.32 added together 0.16+0.32/4 = 0.12 but when i carried out a figure of 8 i got 0.07 on all outlets could this be because the different types of earth conductor any thoughts please
 
With L and N readings of 0.16 (which are abit low IMO) i'd be expecting a E (if its smaller than L&N) to be around 0.26.

Thus, doing the prediction for R1+R2 (0.16+0.26)/4 i'd be expecting a reading of around 0.11.

When conducting the figure of 8 for R1+R2 making sure you have the L and E of opposite legs connected together, you should be getting around 0.11 at each socket.

The reason you are getting 0.07 is almost definitley going to be parallel paths somewhere. What you must remember, are that when parallel paths are in circuit the reading will be drawn down towards 0 depending on the strength/amount of parallel paths.

Try disconnect the boiler and go again.
 
Either you have a good ring because you can allow 0.05 reading either way for external factor temp and loose connection or good connections even Orr you have a interconnection a ring with in a ring. Did you take a reading at ever socket on the circuit then?
 
I was just trying to put it, as you would if the installation was installed properly. However, i agree Richard it sounds like the ring main will resemble a spaghetti bolognaise.
 
Thats worth a look at the thing is the installation is of age not sure what under the floor the IR is good and the customer i don't think wants to have this looked at the same old story
 
If you for your figure of 8 at the fuseboard the parallel paths shouldn't come into it. It is likely it could be a 'spider' ring with a short ring with many spurs to sockets. IMO I wouldn't worry to much if you get good readings at each point
 

Reply to Ring Final Circuit Problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
795
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
I am not a qualified electrician, I was employed as an electrician after my MoD electronics apprenticeship but that was 30 odd years ago. So I...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock