I'll probably receive cries of abuse that this query was dealt with years ago but not when I was in the forum so........When testing ring can anybody think of a reason why the ring final tests (R1,R2 and Rn + link test) shouldn't be done from the back of a socket or other outlet on the ring. As you'll all be aware it's sometimes bloody difficult to work in CCU in back of a cupboard and in particular to identify correct cables for the link test. It would be much easier from back of socket etc.
 
You could save yourself a little confusion, by checking the number of conductors entering the fuse holder/mcb at the origin before making the test at the socket.

However, one small disadvantage is likely to be the inability to identify the circuit at the ccu and order of circuit conductors
 
GN3
continuity of ring final circuit conductors are undertaken at the DU or CU.
Also see 612.2.2

Also how would you know the PD is suitable for the type of wiring etc?
 
agree with Amp David, it is sometimes a lot easier (and safer) to conduct the test at a fitting, particularly if access and lighting are an issue.
 
When conducting PIR's your going to come across CU 's which are crammed full and a total mess!

So what do you do re the testing of RFC!

IMO trying to locate the ends of the CPC's and neutrals can introduce faults in the board and can cause you grief so I carry out the tests at suitable socket outlets knowing that the results will include parallel paths and the neutral is still connected so IR tests are affected!

I would like to carry out these tests at the CU but sometimes this is just not possible.

When filling in the EICR the above can easily be documented along with all of your other observations and recommendations about the premises especially Item 4.1 on the schedule.

I am sure others will have very different veiws on the subjest!
 
tony mc, I agree.

re 612.2.2, doesn't specify where the test should be done.

I think it's a good case for marking all the conductors in DBs with circuit identification...Amd 2??? :)
 
Here's an example, singles in trunking...

Neutrals appear to be in correct order, but would you trust that they are?
I wouldn't, bearing in mind that the place was in use, so powering down circuits willy nilly, or disconnecting neutrals on a live circuit, wasn't an option. Customer would go mental!
 

Attachments

  • P1000185s.jpg
    138.1 KB · Views: 227
off topic !, when i do installs with singles i always label all cores inside the DB ie on the phases, phase colour and circuit number, neutrals and CPC circuit number
 
Thanks for helpful replies Guys and Gals. I am not confused and I always identify the conductors where they leave the fuse carrier/breaker. The problem is seeing which conductor goes into which sheath further back and often behind the CCU. As you'll all be aware it's much easier to see both sheaths behind (most) sockets and there's more room. Electrically I can't see any reason why not. A ring being just that; it doesn't seem to matter where you test it. Or am does anyone know different.
 
The false IR readings is the only thing I can think of, you could whip the cover off the CU anyway to check the PDs but if you have it open you may as well test from there as there's always choc block to extend the cables temporarily to a useable length
 
In larger DB's, and singles in trunking, I almost always carry out ring final tests at an outlet. The readings will be no different, and it is generally much easier to disconnect and test at an outlet than some DB's.

With regards to parallel paths, you will also get them at the DB if they exist. Take a trunking / conduit system, all sockets will be linked by their CPU and the metal work.
 
i tend to agree with adam but it could be safer testing at the c/u because you being remote from the c/u and if someone switched the circuit on while you were holding the phase conductor. I know its a long shot but it could happen.
 
i tend to agree with adam but it could be safer testing at the c/u because you being remote from the c/u and if someone switched the circuit on while you were holding the phase conductor. I know its a long shot but it could happen.

Safe Isolation includes locking off the circuit so that's just not a possibility;)

:thumbsup
 
i use both methods depending on circumstance. I asked the same question of the forum about 2 yerars ago. I even do it sometimes on initial verifications, to save messsing with the lovely neat board somebody, or myself has wired. Theonly ossibility of danger using this method (assuming the mcb IS LOCKED OFF) is that you could have the ends of the ring terminated into different MCB's
 
On my Elecsa Assessment last year I was asked to carry out an end to end continuity test on a ring final circuit. I asked "Do you mind if I carry this out at a socket outlet as I would prefer not to disturb my nice neat wiring" :)

The assessor said that this was fine :thumbsup
 

Reply to Ring final test from socket??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
810
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock