I was called to a friends flat today after he had heard a big bang from the ring main. He said he checked the CU and the MCB was tripped, so not knowing anything about electrics he put it back on, he said it stayed on for a couple of seconds then tripped again. I went round to have a look and carried out a meg test on the circuit. L - E fine, N - E fine but the L - N is showing a dead short. Reading was 0.00. I checked that i had unpluged everything and i had. Circuit is run in singles and in metal conduit in concrete floors and walls. Im going back tomorrow to investergate further but has anyone got any ideas what it could be ?
ah its a bugger when its in conduit like that! my approach would be take one leg of the ring out of the consumer unit then start at each accessory, disconnect each accessory and IR test each link one by one untill you get a clear reading, i had this once, turned out a spur out the back of socket was supplying an outside light filled with water :eek: other than a dodgy spur or hidden appliance still plugged in? good luck anyway!
Reply to Ring main fault in the Australia area at ElectriciansForums.net
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...