Hi, Im a bit puzzled, recently did a new kitchen install with complete new wiring from the cu, this included a kitchen ring, upon testing I have continuity on the n to n end amd cpc to cpc but no continuity on the live ends, Insulation resistance checks out fine on investigation using the half test method, so im confused to as why this is?
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
If there’s no continuity, you’ve got a split ring somewhere mate.
 

Sintra

Admin
Supporter
Can you explain what the half test method is? If you have any fcu’s on the ring final you might have one of the lives in the output side accidentally
 

Baddegg

-
Arms
Supporter
Esteemed
Had that before, kitchen fitter tiled over 1 sfcu outlet leaving 2 of the 3 exposed....he was popular
 
  • Thread Starter Thread Starter
  • #6
Can you explain what the half test method is? If you have any fcu’s on the ring final you might have one of the lives in the output side accidentally
Can you explain what the half test method is? If you have any fcu’s on the ring final you might have one of the lives in the output side accidentally
Hi all thanks for the quick responses, ive taken all faces off to check the connections which is all fine, its a small kitchen diner with only 6 sockets and a FCU, so I know the cable routes, ive split the ring at the mid point and checked IR which checks out fine, I didnt have time to do a full check, im just wondering if the next best thing is to disconnect both legs at the board, connect the line to the earth of one leg and check for continuity at the sockets themselves, then eliminate the issue by repeating the method of halfing the circuit.
 

Baddegg

-
Arms
Supporter
Esteemed
Hi all thanks for the quick responses, ive taken all faces off to check the connections which is all fine, its a small kitchen diner with only 6 sockets and a FCU, so I know the cable routes, ive split the ring at the mid point and checked IR which checks out fine, I didnt have time to do a full check, im just wondering if the next best thing is to disconnect both legs at the board, connect the line to the earth of one leg and check for continuity at the sockets themselves, then eliminate the issue by repeating the method of halfing the circuit.
Did you first fix before the Kev turned up?
 

Taylortwocities

-
Arms
Esteemed
I don’t know why you bothering with IR tests. An IR test on a complete open circuit is going to give ok results.

You have a Continuity problem.
I have had lengths of cable with breaks in the copper inside the insulation.
it’s a standard process - split the circuit and narrow it down. Have fun!
 
Would it not be easier to use a wander lead, connect to one leg of the line at the CU and test for continuity on the line at the backs of all accessible points until you find the break in continuity?
 
  • Thread Starter Thread Starter
  • #10
I don’t know why you bothering with IR tests. An IR test on a complete open circuit is going to give ok results.

You have a Continuity problem.
I have had lengths of cable with breaks in the copper inside the insulation.
it’s a standard process - split the circuit and narrow it down. Have fun!
That is true now I come to think of it 😂
Post automatically merged:

Would it not be easier to use a wander lead, connect to one leg of the line at the CU and test for continuity on the line at the backs of all accessible points until you find the break in continuity?
Normally I would use this method but due to the distance of the run i cant unfortunately.
 
I often IR test between the two ends on open continuity to see if there is a tenuous connection or if it is just open.
 
disconnect both legs at the board, connect the line to the earth of one leg and check for continuity at the sockets themselves
I would do this. I wouldn't bother splitting the circuit. You installed it so you know the route it takes, follow one leg out, testing at each socket as you go. I'd use my R2 adaptor to speed things up.
 
  • Thread Starter Thread Starter
  • #13
I would do this. I wouldn't bother splitting the circuit. You installed it so you know the route it takes, follow one leg out, testing at each socket as you go. I'd use my R2 adaptor to speed things up.
Due to the run of the cable from the cu to the kitchen is restricts me from the r2 method so I was thinking if I connect the line to earth at the db of leg 1 at the board and then use my multifucntion tester with the plug attachment at each socket this should narrow the problem down?
 

Taylortwocities

-
Arms
Esteemed
Yes. Connect one leg to earth at the cu, disconnect the other leg too.
you can then do continuity tests between earth and line at each socket etc.
Blimey, don’t they teach people this basic stuff anymore?
(sorry, not having a go at you,specifically. )
 
  • Thread Starter Thread Starter
  • #15
Yes. Connect one leg to earth at the cu, disconnect the other leg too.
you can then do continuity tests between earth and line at each socket etc.
Blimey, don’t they teach people this basic stuff anymore?
(sorry, not having a go at you,specifically. )
No I totally agree mate, during my apprenticeship I never really came across any fault finding so I have a little experience, also in college we never really went into depth on it so Its the things like this they need to teach more at college, I know you get more from the actual on site experience but if you dont come across it then its not something you will know but I get what youre saying.
Post automatically merged:

No I totally agree mate, during my apprenticeship I never really came across any fault finding so I have a little experience, also in college we never really went into depth on it so Its the things like this they need to teach more at college, I know you get more from the actual on site experience but if you dont come across it then its not something you will know but I get what youre saying. Cheers for the reply, appreciate it
 
Spilt ring set up r1+r2 as if it's a radial. Test at each socket when you loose r1+r2 continuity your issues is between that outlet and last. But you do have to figure out the correct socket order.
 
Due to the run of the cable from the cu to the kitchen is restricts me from the r2 method so I was thinking if I connect the line to earth at the db of leg 1 at the board and then use my multifucntion tester with the plug attachment at each socket this should narrow the problem down?
Yeah, that's what I meant. This is the R2 adaptor, it'll save you taking off the sockets:

Post automatically merged:

Plug adaptor = R2 adaptor, same thing
 
  • Thread Starter Thread Starter
  • #19
Yeah, that's what I meant. This is the R2 adaptor, it'll save you taking off the sockets:

Post automatically merged:

Plug adaptor = R2 adaptor, same thing
I get you! Appreciate the response
 

ipf

-
Mentor
Arms
Esteemed
No I totally agree mate, during my apprenticeship I never really came across any fault finding so I have a little experience, also in college we never really went into depth on it so Its the things like this they need to teach more at college, I know you get more from the actual on site experience but if you dont come across it then its not something you will know but I get what youre saying.
Post automatically merged:
Well you've come across it now.... and it's called on site experience;)
 

Reply to Ring main no continuity on live ends in the Electrical Forum area at ElectriciansForums.net

Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Top Bottom