Discuss Ring mains continuity test-problem in the UK Electrical Forum area at ElectriciansForums.net
I
isaiah64
Good day,
Just a quick one, on testing a ring main continuity test. After following the following sequence on a existing circuit.
he problem have is on my Cpc - Cpc. The reading I am getting s open circuit. But when test L1-Cpc2 and L2 - Cpc1 he reading am getting is inconstant. Would appreciate in input in my question as I am probability just missing something small.
My conclusion on this is There I a lose connection and the way to fix it is to do a r2 test between the connections on the ring.
Test
L1 - L2
N1 - N2
Cpc1 - Cpc2
Then
L1 - N2
L1 - N1
Then
L1 - Cpc2
L2 - Cpc1
If your r2 result is showing open circuit then you are correct that there is no end to end continuity on the ring cpc and as you say most likely due to a loose connection.
Using the R2 wander lead method of testing from one leg of the cpc to the earth of each socket should show the sockets up to which that leg is connected at the socket where you lose continuity the disconnection will be either at that socket or at the one just before it in the ring.
How many sockets are we talking about? Visual inspection is the way forward here. Chances are if the earths have come out the terminals, then other connections may also be dodgy.
20 sockets? 5 min a socket ? Less than 2 hours and all is checked, sleep easy!
If the circuit is already live its worth a quick walk around doing a Zs at each and every outlet on the circuit and see if if you get a "big" difference between 2 sockets - if so try these first.
If the circuit is not live yet, don't try the above idea.
Thank you for the advise, found fault. Fault was found by use of r2 wondering lead. Lose connection! HAHA.
or interest sake I used the loop impudence method and fault was also detected as the reading between socket was mjor difference.
thanks
well, at least you didn't have to go lifting floors and chopping walls out. lol. cheers for getting back with a result.
Reply to Ring mains continuity test-problem in the UK Electrical Forum area at ElectriciansForums.net
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
  • Locked
Currently I have a spur from the ring main, but I'm planning on adding more sockets. I can't add a 13 amp fuse because I expect to be using more...
5K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...