Not getting continuity on r1, rn and r2.

But the sockets are working fine,

Amy ideas what the issue could be, I'm checking behind each socket.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members

loz2754

-
Esteemed
Arms
Reaction score
1,505
Are you sure it's a ring final circuit? If so, then I'd be looking for recent alterations or additions, to see if someone has broken the ring.
 

Strima

-
Esteemed
Arms
Reaction score
5,562
As above, could be two radials.

What size is the OCPD?

Even with no continuity the sockets will work fine, but the conductors may well be undersized for the protective device. Also you may have a couple of live conductors flapping around somewhere.

Easiest way to find the break is to isolate the circuit, link out L-E at the board end on one leg and test at each socket for continuity between L-E at each socket until you find one with no continuity, this will either be the break or the socket before it. Same for N-E.
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
62,632
needs first to determine whether it should be a ring or 2 radials. map it out on continuity resistance values then go from there.
 

Iona222

Trainee
Reaction score
1
Could it be a "spider ring", where sockets are spurred of junction boxes in the ceiling/floor void? How old is this installation?
It's about 40 year old mate, I couldn't find the fault in the ring, I told the client . There's spurs running everywhere.
 

SJD

-
Mentor
Esteemed
Arms
Reaction score
1,805
I think we could do with a bit more specific info.

Firstly, what size is the circuit breaker or fuse? And what is the cable - e.g. 2.5mm2 twin & earth, or 4mm2, or something else?

Secondly, why were you measuring ring continuity - is there some fault you were asked to find, or planned to add more sockets, or some other reason?
 

Iona222

Trainee
Reaction score
1
I think we could do with a bit more specific info.

Firstly, what size is the circuit breaker or fuse? And what is the cable - e.g. 2.5mm2 twin & earth, or 4mm2, or something else?

Secondly, why were you measuring ring continuity - is there some fault you were asked to find, or planned to add more sockets, or some other reason?
Its 32amp 2.5 twin earth. Its supposed to be a ring and it looks like a ring. I wasn't able to resolve the issue for the client, I told her, as you can see I'm a trainee, so I would like to know the best way forward of I come across this situation, would I just split the ring into radisls?
 

Iona222

Trainee
Reaction score
1
I think we could do with a bit more specific info.

Firstly, what size is the circuit breaker or fuse? And what is the cable - e.g. 2.5mm2 twin & earth, or 4mm2, or something else?

Secondly, why were you measuring ring continuity - is there some fault you were asked to find, or planned to add more sockets, or some other reason?
I was asked to repair the fault, no continuity.
 

westward10

Admin
Mod
Esteemed
Reaction score
17,948
Never assume 2 × 2.5 conductors are going to be a ring final circuit. You need to verify where each "side" goes. What I do is disconnect all conductors and link out the line and cpc of one of the cables then see which of the sockets are measuring continuity between these conductors, repeat with line and neutral linked out and see if the same sockets correspond. Mark these on a rough plan, repeat with the other cable, if they are separate radials you should have no cross over between the sockets.
 