I'm building a new property consisting of 4 sperate discrete buildings, all roughly in a straight line. My question: Is there any advantage to connecting the buildings supply in a ring rather than just daisy-chaining them (i.e. radial)?

I was planning to run a single 1 AWG backbone supply up the middle of the property and spur off each building (radial). However I'm concerned about the last building seeing voltage fluctuations when the first building has high current loads... So instead if I run 2 x 4 AWG in a ring configuration would this benefit from reduced voltage fluctuations at the extremities?

20220228_093751.jpg
 
Last edited:
You can run some calculations to see the effects for any combination with a bit of time and a spread sheet! But you also should factor in the supply impedance as you will always have that as a common factor no matter what layout you consider.

You need to be careful if the total load is more than the #4 AWG cable can handle that is will be reasonably distributed around the buildings neither 'leg' gets too much current.

Using 4 separate sub-mains to each building would solve the between-building effects, but not heavy loads in the same building impacting on the supply. Also more cable costs!
 
What currents and distances are you looking at? The usual requirement in the UK is for no more than 5% voltage drop, or 3% for lights (but with LED that is a bit out of date). On longer cables that can become a bigger sizing factor than the current carrying capacity (ampicity).
 
What currents and distances are you looking at? The usual requirement in the UK is for no more than 5% voltage drop, or 3% for lights (but with LED that is a bit out of date). On longer cables that can become a bigger sizing factor than the current carrying capacity (ampicity).
Many thanks. In total it will be 70 amps for all 4 buildings on 220v (with building "M" having the highest loads). The longest distance from supply to Bed 1 is around 400ft. I've been working on calcs to keep drop below 4%
 
You can run some calculations to see the effects for any combination with a bit of time and a spread sheet! But you also should factor in the supply impedance as you will always have that as a common factor no matter what layout you consider.

You need to be careful if the total load is more than the #4 AWG cable can handle that is will be reasonably distributed around the buildings neither 'leg' gets too much current.

Using 4 separate sub-mains to each building would solve the between-building effects, but not heavy loads in the same building impacting on the supply. Also more cable costs!
I've run some calculations for various scenarios like you suggested...I just assumed that ring would be better and that's why I'm asking on the forum for confirmation... But having run a few scenarios I can't see the benefit at all (and in some scenarios radial gives smaller losses!)

So simple 1 AWG radial it is then (don't want to run 4 sub-mains since the cable cost will be massive)
 
The ring has advantages for loads that are physically in some sort of a ring!

In the UK we have a "ring final circuit" that is only seen in countries that used fused plugs, so basically the UK and a few related countries. But that makes sense as you have a single 32A breaker feeding any number of sockets connected as a ring, with each socket able to deliver up to 13A (but with smaller fuses like 3A common for low power items). Here we slightly under-size the cable (2.5mm rated 20A) on the basis the loads are limited and distributed leading to less copper costs, and due to the double paths a more reliable/redundant earth. Typically a RFC is limited to 100m^2 area, or commonly one per-floor to limit the impact of a fault.

Where you also see a ring layout in the UK is for high voltage distribution in a city. But there the ring is normally left with a link point open (so two radials in use, typically lowering the max fault current) then the link points can be changed to close one and open another two leaving one segment of cable isolated, etc.
 

Reply to Ring vs Radial for minimum voltage fluctuations in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
I'm in the process of building a new house (West Indies). Due to terrain it is a modular design where each bedroom is an individual building...
Replies
4
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K
Hi guys I'm a bit frazzled by the wording on the main project. So, we are told to keep the max circuit length down to 30m, tutors said that isnt...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock