Hi forum, has anybody on here had an issue with the rolec 1 way 16amp touring outlet isolator?
The isolator does not operate when the 16amp plug is inserted as the plug does not appear to push the interlock far enough back to release the isolator.
Out of six units 3 do not work.
Any feed back from installers of these would be great thank you.
 
Are the units the ready built ones from Rolec, or did you add the sockets to an existing box?

If they came complete, get rolec to fix

Otherwise can you cut a few mm off the end of the socket to let the plug push further in?
 
Are the units the ready built ones from Rolec, or did you add the sockets to an existing box?

If they came complete, get rolec to fix

Otherwise can you cut a few mm off the end of the socket to let the plug push further in?
Yes they are the ready built ones from rolec but after contacting them twice now there customer service appears a bit lapse,
I was just putting the issue out there as they must sell and produce a lot of these units as they have changed them to comply with the 18th edition, and previously I have installed the non isolation version with no issues.
 
Yes, it does not alter the supply arrangement, but it would not be very good for charging your vehicle in the day lol..
 

Reply to Rolec 1 way 16amp touring outlet problem in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
661
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
833
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
482
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock