Hi all, after some advise please.

I work as a maintenance engineer at a school and recently we had an outside contractor come in and fit an external Rolec EV unit to the outside of our workshop under the grant scheme.

I don't know much about the installation of these units but I did do part P several years ago so I have some electrical understanding. Consequently I do have some concerns about the installation which may be an issue or maybe more likely just my lack of knowledge!

The EV unit has the internal RCD for the AC supply, and the seperate RCD module for any DC injected back into the circuit. It has been installed with an internal isolator, meter and comms box which all seems fine.

However,

1) The contractors installed a new circuit in our DB for the EV supply but there is no test certificate to show results.

2) The unit is installed in our yard where we store gas cylinders and fuel. The charging unit has been installed directly above a metal storage unit that contains gerry cans of petrol. Gas cylinders are housed in a cage about 2 meters away.

3) The earth from the EV unit has been connected to the building's steel rainwater downpipe which goes under the ground but I've no idea how deep the pipe goes.

Are these issues cause for concern?

I'd appreciate your thoughts.

Many thanks.
 

Attachments

Aico 3000 Range
This official sponsor may provide discounts for members
Regarding the earthing, it's been connected to the Lightning Protection which isn't ideal but if it's working properly it'll have an overall resistance to earth of less than 10 ohms. I presume you do have the LP system maintained?
 
  • Thread Starter Thread Starter
  • #3
Regarding the earthing, it's been connected to the Lightning Protection which isn't ideal but if it's working properly it'll have an overall resistance to earth of less than 10 ohms. I presume you do have the LP system maintained?
Yeah, the LP system is maintained by a specialist contractor.
 
Yeah, the LP system is maintained by a specialist contractor.
Can't see an issue with the earthing then unless someone else knows something I don't

Complete side note the way they've drilled the RWP to bond it is something I've only seen a couple of times... Very lazy!
 

Sintra

Admin
Supporter
2) The unit is installed in our yard where we store gas cylinders and fuel. The charging unit has been installed directly above a metal storage unit that contains gerry cans of petrol. Gas cylinders are housed in a cage about 2 meters away.
Surely someone from the school would have chosen the location for the charger.
 

Wilko

-
Arms
Esteemed
Hi - hopefully whoever has engaged the Electrician has the Electrical Installation Certificate. It’d be interesting to see the loop impedance :) .
 

Midwest

-
Arms
Esteemed
Hi - hopefully whoever has engaged the Electrician has the Electrical Installation Certificate. It’d be interesting to see the loop impedance :) .
You would think so, but at my place new circuits have been installed to supply some AC units in apartments, not a sniff of an EIC and we won't mention compliance certificates.

Edit By the by @Nuttyoak what supply do you have?
 
  • Thread Starter Thread Starter
  • #8
Surely someone from the school would have chosen the location for the charger.
Yeah, the bursar.
Post automatically merged:

You would think so, but at my place new circuits have been installed to supply some AC units in apartments, not a sniff of an EIC and we won't mention compliance certificates.

Edit By the by @Nuttyoak what supply do you have?
The DB is 3 phrase which is run from the switch gear in the main plant room. The earth is also run from the plant room but I do not know what the earthing arrangement is at the incoming source. I do know we don't have our own sub station which is something we are apparently looking at because the site is so large in both the area it covers and the demand required. We've had issues with volt drop at the furthest corners of the school.
 
Last edited:

davesparks

-
Mentor
Arms
Esteemed
1 Yes an electrical installation certificate should have been completed and issued to the person ordering the work.

2 personally I think that is a daft place to install it and if I had been doing the job would definately have questioned the location. Whilst it should be absolutely fine and is unlikely to be a problem I would err on the side of caution.

3 it's not right, the lightning protection system should be bonded to the Electrical Installation at the main earth terminal and that bond should be connected underground at one of the earth rods. The odd connection they have made could cause a lightning strike to partially divert via the EV charger circuit.
If the LPS is correctly bonded then it will act as a very good earth electrode for the installation sufficient to allow even a PME earth to be used for the charger.

I suspect the installers take a one size fits all, monkey see - monkey do, approach to these installations without applying any thought to the job.
 

DPG

-
Arms
Esteemed
Advent Win
I'd personally move the fuel bin. Doesn't seem ideal to have it where it is.
 
I don't know the ins and outs of LPS which are essentially a stand alone safety system aside from the recent requirement for it to have a main protective bond to reduce pass over in the event of a fault, the chances of the original specification to allow it to be used for another purpose are all but zero.
Post automatically merged:

Do you have a 12 monthly test of the LPS.
 
Last edited:
  • Thread Starter Thread Starter
  • #13
I don't know the ins and outs of LPS which are essentially a stand alone safety system aside from the recent requirement for it to have a main protective bond to reduce pass over in the event of a fault, the chances of the original specification to allow it to be used for another purpose are all but zero.
Post automatically merged:

Do you have a 12 monthly test of the LPS.
Yeah, we do.
 
That's great be interesting to see what they make of this ad hoc connection.
I do this all day every day and I wouldn't say anything about it - if I saw this during an inspection I'd just assume it was a bond to the electrical earth as would my colleagues
 
I do this all day every day and I wouldn't say anything about it - if I saw this during an inspection I'd just assume it was a bond to the electrical earth as would my colleagues
That could well be a natural assumption, do you never verify this. Would this not be deemed an important part of the inspection??
 
Last edited:

davesparks

-
Mentor
Arms
Esteemed
Do you have a 12 monthly test of the LPS.
Our LPS is required to be tested on an 11 monthly cycle to keep track of any season variations.
Ive never known if this is normal or a peculiarity of our storage license.
Post automatically merged:

I do this all day every day and I wouldn't say anything about it - if I saw this during an inspection I'd just assume it was a bond to the electrical earth as would my colleagues
But it appears to be undersized for the size of the installation and its above ground when it should be below ground level at an earth rod termination.
 
That could well be a natural assumption, do you never verify this.
We don't have enough time really, some days I have 5+ inspections to do and if something isn't going to affect the LPS I can't justify investigating further

My view is that it's down to the electrician who made the connection to determine whether it's safe or not
 

davesparks

-
Mentor
Arms
Esteemed
We don't have enough time really, some days I have 5+ inspections to do and if something isn't going to affect the LPS I can't justify investigating further

My view is that it's down to the electrician who made the connection to determine whether it's safe or not
How can you thoroughly inspect 5 sites in a day?
How do you know if it isn't going to affect the LPS if you don't investigate?
 
We don't have enough time really, some days I have 5+ inspections to do and if something isn't going to affect the LPS I can't justify investigating further

My view is that it's down to the electrician who made the connection to determine whether it's safe or not
I find that an odd reply as few electricians are conversant with the Regulations you are testing to. I would suggest time factors are not relevant. So knowing the relevant requirements is this an acceptable situation.
 
Our LPS is required to be tested on an 11 monthly cycle to keep track of any season variations.
Ive never known if this is normal or a peculiarity of our storage license.
Post automatically merged:



But it appears to be undersized for the size of the installation and its above ground when it should be below ground level at an earth rod termination.
11 monthly is correct to BSEN 62305 to account for seasonal changes in ground conditions as you say.

I don't know if it's undersized because it's for the earthing of the EV charger nothing to do with the LPS but we would connect an EQ bond wherever possible you can't always get it underground.
Post automatically merged:

How can you thoroughly inspect 5 sites in a day?
How do you know if it isn't going to affect the LPS if you don't investigate?
You just develop the speed over the years. Lightning Protection can be complex on things like refineries which can take weeks to inspect but general systems for example a block of flats with 15 downconductors it would take 30-40 minutes to inspect the air termination network and maybe another 30-40 minutes to test the earth rods. With the recent obsession with compliance testing we are flooded with work and you wouldn't last if you couldn't keep up.

I don't know how to answer your other question, not much shy of vandalism will stop LP from working if it's maintained.
Post automatically merged:

I find that an odd reply as few electricians are conversant with the Regulations you are testing to. I would suggest time factors are not relevant. So knowing the relevant requirements is this an acceptable situation.
I don't know if it is acceptable or not. I wouldn't bat an eyelid if I saw this on a job but that being said, it is not really appropriate to connect it where it is as it's likely to get disturbed which I guess could cause the EV charger to not be earthed?
 
Last edited:

Midwest

-
Arms
Esteemed
Hmmm, interesting. We have a lightning system. In the 15 months I’ve been there, never seen it tested. Are all LPS the same, or is the testing only required for petrochemical establishments for example?
 

davesparks

-
Mentor
Arms
Esteemed
Hmmm, interesting. We have a lightning system. In the 15 months I’ve been there, never seen it tested. Are all LPS the same, or is the testing only required for petrochemical establishments for example?
The BS quoted above covers all installations, so yes they are all the same.
 

Reply to Rolec EV installation in the Electrical Forum area at ElectriciansForums.net

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Top Bottom