farmerian

Im currently doing 2395 inspection and testing course and was wondering When doing rule of thumb of 0.8( correction factor) for Zs values do you apply this to all books e.g bs7671, on site guide, and guidance note 3 ? I allways believed you dont for guidance note 3 but tutor says over wise
 
Im currently doing 2395 inspection and testing course and was wondering When doing rule of thumb of 0.8( correction factor) for Zs values do you apply this to all books e.g bs7671, on site guide, and guidance note 3 ? I allways believed you dont for guidance note 3 but tutor says over wise

You only apply the 0.8 correction factor to the tables in BS7671, this is because those tables are done for 70 degrees C operating temperature. The OSG tables have been corrected for 20 Degrees C, and do not need correcting.

Your tutor needs a lesson in basic electrical theory.

temperature increases, resistance increases, and vice versa for lower temp, remind him, before you all screw up your exams,

Cheers............Howard
 
^^^ as above,
G.N. 3 and on-site guide are corrected values. For bs7671 values use the 80% rule.
Good luck in your exam buddy,
and give your tutor a lesson ;)
 
Those who can do, do ..... those who cant teach!

OK, not entirely true, there are some very good ones out there. But you do make a valid point about some lecturers and their apparent lack of knowledge. The frighteneing thing is they are educating the next generation of "electricians" who bank everything the say!!
 

Reply to Rule of thumb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
885
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
943
Hi this is my first post, I’m looking for some advice I’m doing my Inital verification course as part of my NVQ. I’ve passed the practical part...
Replies
2
Views
1K
Hi all, I done my am2 and passed everything except testing and inspect, i failed on Zs (earth fault loop impedence). It says I did not correctly...
Replies
10
Views
5K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock