BathSparks
Hello fellow sparkys
The customer would like me to install A small 2 way CU in his garage. This is for him to use a few power tools, lights and possible an electric door motor. The Armoured cable run is about 25 metres. I am planning to put an RCBO in the house C.U. to protect to cable to the garage.
All's well so far. He showed me his House CU, a 12 way Hagar board with RCD protection on All circuits. A previous electrician had by-passed the RCD and told the customer it was faulty. This I intend to re-instate (with new RCD if necessary). There will be one way spare in the board after I remove an old cable (dodgy 1.5mm cable that went to garage for a light) to install the new circuit and RCBO
The question is this: Do I install the RCBO in the slot even though this is protected along with all other circuits by an RCD. The RCD at the garage end could cause "discrimination" problems between the two. One solution would be to use a Henley block and split the tails to another main switch/RCBO and run the garage circuit from this. I cannot split the bus-bars in the old CU because there are not enough ways.
Another solution would be to try to persuade the customer to have a new 17th edition CU with all the benefits this brings. This, however tends to elicit the response "It has been working fine for the last xxxx yrs" Given that the Armoured cable will probably cost £60 or £70 + £50 for the garage mini CU, the cost is adding up. Any helpful suggestions?
The customer would like me to install A small 2 way CU in his garage. This is for him to use a few power tools, lights and possible an electric door motor. The Armoured cable run is about 25 metres. I am planning to put an RCBO in the house C.U. to protect to cable to the garage.
All's well so far. He showed me his House CU, a 12 way Hagar board with RCD protection on All circuits. A previous electrician had by-passed the RCD and told the customer it was faulty. This I intend to re-instate (with new RCD if necessary). There will be one way spare in the board after I remove an old cable (dodgy 1.5mm cable that went to garage for a light) to install the new circuit and RCBO
The question is this: Do I install the RCBO in the slot even though this is protected along with all other circuits by an RCD. The RCD at the garage end could cause "discrimination" problems between the two. One solution would be to use a Henley block and split the tails to another main switch/RCBO and run the garage circuit from this. I cannot split the bus-bars in the old CU because there are not enough ways.
Another solution would be to try to persuade the customer to have a new 17th edition CU with all the benefits this brings. This, however tends to elicit the response "It has been working fine for the last xxxx yrs" Given that the Armoured cable will probably cost £60 or £70 + £50 for the garage mini CU, the cost is adding up. Any helpful suggestions?