Discuss S-type RCBOs in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
20
Does anyone make S-type RCBOs?

For discrimination you should use an S-type RCD to protect a sub-main feeding a CU with a normal 30mA RCD or RCBOs. This can be handled with a 100mA 100mSec S-type RCD. It would be convenient if this were combined with a type B or C 63 amp MCB.

This is in a domestic context with a main DB feeding a number of CUs.
 
RCD required on submain consisting of 16mm2 T&E (not SWA) which is <50mm from surface of stud wall. Really you should use 30mA but then you don't get discrimination.

There's no "should really use" about it. If you are complying with the regs it has to be 30mA.

I'd be redesigning the distribution circuit installation myself.
 
I doubt you will find delayed 100mA RCBOs, certainly not in a domestic capacity.
You should have designed the submain to not require RCD protection.
Doing your method of delayed 100mA RCD protection will not meet the regulations.

EDIT: beaten to it by Andy78
 
RCD required on submain consisting of 16mm2 T&E (not SWA) which is <50mm from surface of stud wall. Really you should use 30mA but then you don't get discrimination.

Only 30mA non time delayed RCD protection is allowed for this application.

Presumably this domestic installation is split across multiple CUs? If so the having a single RCD protecting each CU is not really a problem as far as the regs are concerned.
For example, if you have an installation spread across two CUs each with an RCD main switch is it any different to having the whole lot on one split CU with 2x RCD?
 
Thanks for the comments. The submains already existed probably since pre-17th edition days protected by 63 amp MCBs. A risk analysis might suggest that the S-type RCDs would be better than none at all. It may be possible to change some of the more accessible cables for SWA which would solve the problem for some of them

But anyway thanks for the confirmation that S-type RCBOs are probably unavailable.
 
Thanks for the comments. The submains already existed probably since pre-17th edition days protected by 63 amp MCBs. A risk analysis might suggest that the S-type RCDs would be better than none at all. It may be possible to change some of the more accessible cables for SWA which would solve the problem for some of them

But anyway thanks for the confirmation that S-type RCBOs are probably unavailable.

As said, this will not comply with the requirements of BS7671 for alterations to existing circuits. You can either provide 30mA protection for the distribution circuits, change the installation of the distribution circuits so they do not require additional protection, or leave it as it is.
 
but is it necessary to RCD protect the sub-main feeds if they complied with previous edition/s of regs.?
 
A risk analysis might suggest that the S-type RCDs would be better than none at all. .

Would it? If you take the purely mathematical view of the situation then it does appear that way. But what if you actually think about the purpose of the RCD?
30mA RCDs are designed to operate before death occurs in a person making contact with a live conductor, any delay in the operation and they will not disconnect before death has occurred.
Any RCD which operates after the death of the person might as well not be there at all from the point of view of that person.
 
Last edited:
The 30mA RCD requirement is to (hopefully) prevent a fatal shock. A time delayed 100mA RCD doesn't do that, so you're wasting your time and money.

Add mechanical protection, re-route the submain, or change it for a cable type which will comply.

Protecting a sub-main with a 63A MCB is unlikely to offer discrimination for a downstream MCB anyway.

That's why switch-fuses take fuses, not circuit breakers.

I type too slowly!
 
Thanks for all your comments. Looks like a combination of tactics may be required as IssyS says: add mechanical protection where feasible, re-route the submains where feasible, or otherwise change the cables for SWA. Whatever tactic is used, the S-type RCDs don't add any useful additional protection and therefore the question I asked of whether S-type RCBOs are available is irrelevant.
 
Thanks for all your comments. Looks like a combination of tactics may be required as IssyS says: add mechanical protection where feasible, re-route the submains where feasible, or otherwise change the cables for SWA. Whatever tactic is used, the S-type RCDs don't add any useful additional protection and therefore the question I asked of whether S-type RCBOs are available is irrelevant.

Try answering my question!

If the distribution circuit is existing why are you looking to add RCD protection?
 
Why are you dead set against adding 30mA protection to the submains?
If the installation is divided across multiple boards then it's no different to dividing it across a twin RCD split board
 
It's equally likely that each sub main is feeding a complete flat or dwelling so in that situation having a remote 30ma RCD feeding complete CUs would at best be hugely inconvenient in the event of tripping and at worst dangerous.
 

Reply to S-type RCBOs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
887
We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
7
Views
485
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
633
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock