Hi all, looking some advice on s type rcds. Basically can you use them on tt installations for earth fault protection on circuits that don't require additional protection? Know that on a tt installation disconnection times of either 0.2 sec or 1sec must be achieved depending on circuit, but with the delay on the rcd will they be achievable?
Appreciate any advice, thanks!
 
Hi all, looking some advice on s type rcds. Basically can you use them on tt installations for earth fault protection on circuits that don't require additional protection? Yep.
Know that on a tt installation disconnection times of either 0.2 sec or 1sec must be achieved depending on circuit, but with the delay on the rcd will they be achievable? Wont make any diference , disconnection times are for the mcb.
Appreciate any advice, thanks!

Regards Pete.
 
Hi all, looking some advice on s type rcds. Basically can you use them on tt installations for earth fault protection on circuits that don't require additional protection? Know that on a tt installation disconnection times of either 0.2 sec or 1sec must be achieved depending on circuit, but with the delay on the rcd will they be achievable?
Appreciate any advice, thanks!


Let's say it would be prudent to have an up front S type RCD as additional protection on a UK domestic TT system!! lol!!

30mA RCD protection on TT systems are not classified as additional protection, They are a Prime means, as they are generally the ONLY means of achieving TT system max disconnection times. It is the RCD that will disconnect the supply under earth fault conditions, NOT the MBC as has been indicated above....
 

Reply to s type rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
889
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
718
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Replies
3
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock