sparkybrum

Just a quick question, in the general section of this form,

1. presence of under voltage protective devices, there are passive rcds on the cu and no dol starter, I've put n/a for this

2. Connection of single pole devices for protection or switching in line conductors only, all sockets used where DP so I've put n/a for this

3. Particular protective measures for special locations and installations, there is sup bonding to bath so I was ticking this.

Finally routing of cables In Prescribed zones, does this relate to 150mm from ceiling, 150mm from sides etc? And if I'd laid them not in those zones I put n/a?

Cheers guys
 
Just a quick question, in the general section of this form,

1. presence of under voltage protective devices, there are passive rcds on the cu and no dol starter, I've put n/a for this.....would apply only to devices which do not reset automatically on a loss of voltage

2. Connection of single pole devices for protection or switching in line conductors only, all sockets used where DP so I've put n/a for this Are there no single pole devices at all...what about mcb's and light switches?

3. Particular protective measures for special locations and installations, there is sup bonding to bath so I was ticking this.If there is a special location covered by the cert then this applies...only tick if requirements are in place

Finally routing of cables In Prescribed zones, does this relate to 150mm from ceiling, 150mm from sides etc?...and directly in line with an accessory etc And if I'd laid them not in those zones I put n/a?NO!...buried cables must be routed in safe zones or have suitable earthed mechanical protection....if you have installed cables outside these zones without protection this would be a departure

Cheers guys
.................
 

Reply to schedule of inspections help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
Hello all, The Schedule of Inspection forms for an EIC offer you 2 suggestions to enter in the boxes, either a tick to say an inspection has been...
Replies
5
Views
8K
Octopus
O
S
im having a blank moment! when completing a cert for changing a consumer untit (Electrical Installation Cert) is the schedule of inspections...
Replies
1
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock