What code would you give for a Swa supply 3p/N,95mm.
Supplies remote school block,2 storey,no main earth conductor,using sheath,the main earth bonding originates from this Swa,for this block,@ Main Panel board,& is 16 mm
The main earth @ origin is 120mm,Main bonding 50mm.
Cheers
 
Advertisement - Content continues below

Ian1981

-
Mentor
Arms
Esteemed
What code would you give for a Swa supply 3p/N,95mm.
Supplies remote school block,2 storey,no main earth conductor,using sheath,the main earth bonding originates from this Swa,for this block,@ Main Panel board,& is 16 mm
The main earth @ origin is 120mm,Main bonding 50mm.
Cheers
What do you mean no main earth conductor?
You’ve just stated earthing conductor is 120mm
Using the armour for a cpc is acceptable if sized correctly.
What is the earthing arrangement?
Using the armour as a combined cpc/bonding conductor could be acceptable if say it’s TNS
 
  • Thread Starter Thread Starter
  • #3
Swa ,sheath used for main earth,the 120 mm Earth is at the origin intake of the school,this Swa is a sub main,to a remote block.
Tncs is the earthing system,185 mm Tails,120 mm Main Earth,50 mm earth bond.
 
Sheath is not the main earth, it is a cpc. I assume you are doing an EICR so you should know how to Code. What is your opinion.
 
  • Thread Starter Thread Starter
  • #5
Correct a cpc,my opinion is a code 2.
A main earth should have been installed with this Swa,to provide an adequate earth,& Main earth bonding.
 

Ian1981

-
Mentor
Arms
Esteemed
Correct a cpc,my opinion is a code 2.
A main earth should have been installed with this Swa,to provide an adequate earth,& Main earth bonding.
Your opinion is flawed unless inspection and testing revel otherwise.
Have you carried out the appropriate inspection and testing to verify that the current set up is potentially dangerous?

Again it’s a CPC not a MAIN earth

What is the earth arrangement?
Does the distribution circuit have adequate fault protection by ADS for its respective ocpd?
 
Last edited:
  • Thread Starter Thread Starter
  • #8
Yea it’s a cpc the Swa is being used for Main Earth @ the Main Panel in the block.
It’s also being used for the Main earth bonding conductor.
The situation is not potentially dangerous,what are you going on about my opinion is flawed,
The earthing is Pme Tncs.
 

Ian1981

-
Mentor
Arms
Esteemed
Yea it’s a cpc the Swa is being used for Main Earth @ the Main Panel in the block.
It’s also being used for the Main earth bonding conductor.
The situation is not potentially dangerous,what are you going on about my opinion is flawed,
The earthing is Pme Tncs.
I mean you can’t go on opinion, only by proof that it is potentially dangerous
 
  • Thread Starter Thread Starter
  • #11
Ok,it’s been in place since early 70’s,so no it’s not potentially dangerous.
The nitty gritty here is,the sub main to the block.
My opinion is it’s not correctly installed.
The cpc would be ok in protecting the Swa,but not ok to support Main earth bonding.
Code 2
 

Ian1981

-
Mentor
Arms
Esteemed
Ok,it’s been in place since early 70’s,so no it’s not potentially dangerous.
The nitty gritty here is,the sub main to the block.
My opinion is it’s not correctly installed.
The cpc would be ok in protecting the Swa,but not ok to support Main earth bonding.
Code 2
But if you believe it’s not potentially dangerous how can you then code 2 it?
 
  • Thread Starter Thread Starter
  • #13
It’s also a Distribution circuit,thinking a main earth should be present,sized accordingly.
 
Advertisement - Content continues below

Reply to School block Swa supply in the Electrical Forum area at ElectriciansForums.net

Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom