I was wake by a friend to have a look at an Eicr that was done on his rental property .
The Eicr says I quote :
"Due to the c2 codes listed in section k , this report is unsatisfactory. The old consumer unit has type 4 (D) breakers where make it impossible to achieve test results.
So far no problems.
However when I had a look at the " Old "cu it turned out to be metal enclosure Mk split load cu , populated with B type MCB .
Am I missing something ?or was the author of the report trying to " sell" a new Cu as recommended later in report?

Thoughts anyone ?
 
As above ,and if you are certain that the fitted MCB's would have achieved disconnection times there does seem to be an attempt to mislead...
 
Thanks guys, that's what I was thinking .I just wanted to be sure . I will try to upload a picture of the cu later on .
I just wonder if the spark needs to go specsaver and confused the B with a D on the Mcbs marking.
 
MK have never produced type 4 mcbs, not sure why you have D in brackets because they are different and MK never produced these either. What it means difficult to achieve test results I have no idea. Are you sure the board has not been changed since the EICR.
 
It does sound as if there is an error in the report.
Type 4 breakers would be uncommon in a domestic property, but possible. I assume that there are not two consumer units in the property and you have only seen one of them (this would be obvious from the report test results).
I cannot see how type B MK MCBs could be confused for type 4.
 
Thanks guys, that's what I was thinking .I just wanted to be sure . I will try to upload a picture of the cu later on .
I just wonder if the spark needs to go specsaver and confused the B with a D on the Mcbs marking.
If he confused a B with a D then he should steer well clear of EICRs as MK never produced a D anyway. He sounds totally incompetent .
 
There is only one cu in property.
The D is in bracket as quoted in report .
As for being incompetent and steering clear of Eicr , on the report he is described as a qualified supervisor and judging by the name of the company it seems to be specialised in inspection and testing , so I am not sure.Thanks again for all the replies.
 
Hello everyone,
I was wake by a friend to have a look at an Eicr that was done on his rental property .
The Eicr says I quote :
"Due to the c2 codes listed in section k , this report is unsatisfactory. The old consumer unit has type 4 (D) breakers where make it impossible to achieve test results.
So far no problems.
However when I had a look at the " Old "cu it turned out to be metal enclosure Mk split load cu , populated with B type MCB .
Am I missing something ?or was the author of the report trying to " sell" a new Cu as recommended later in report?

Thoughts anyone ?

If someone i thought well enough of,to sleep next to,woke me to discuss MCB characteristics...i would having a test and inspect of our relationship ;)
 

Reply to Second opinion please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Looking to refresh the MCB and RCCB (100A 30mA) units to my 20 year old Contactum P12/100N CU installed in my house. I have presently a...
Replies
2
Views
260
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
675
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
787
The buyer of my house has had an EICR done. I have anonymized and attached. Also the associated quote for remediation. I am wondering: surely...
Replies
26
Views
2K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
78
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock