Discuss Securing cables & trunking to prevent premature collapse. in the UK Electrical Forum area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
Just wondering how your guys observe the reg, for preventing premature collapse of cables in plastic trunking, when securing to plasterboard, i.e. dry lined or plasterboard stud walls?

We’re having some additional fire alarm work carried out, and they mention some ‘clips’ to comply. I was wondering what the clips screw into, plastic raw plugs? Would that be compliant.
 
For mini trunking I screw into joist/stud where possible, or dewalt walldogs direct into plasterboard where not. Screw through a bit of all round band and wrap around cable within trunking
 
If you are having fire alarm work carried out cables should not only be fixed to prevent premature collapse but also that they remain in place so the system still operates. With FP200 this would be to use support suggested by the manufacturer.
 
If you are having fire alarm work carried out cables should not only be fixed to prevent premature collapse but also that they remain in place so the system still operates. With FP200 this would be to use support suggested by the manufacturer.

Yep not sure exactly what cable it is, but think they mentioned FP2000. It’s Chubb, so confident they’ll do it properly.
[automerge]1575021192[/automerge]
Yes, they just screw straight in.

I use D-Line (I think) fire straps, all round band and Schneider do a range of metal T+E clips which is use every third clip or so.

I’ll have to get some to try myself. Surprised they’ll hold in plasterboard by themselves.
 
BS5839:1 quoted fixing of cables to prevent collapse in the event of a fire long before BS7671 and for different reasons. To maintain the system as opposed to persons being tangled in collapsed cables.
 
It's about the only use I've found for them as yet, though they only give a lightweight fixing. If you have any doubts that they'll hold the weight, then it's Fischer cavity fixings.

Problem I have with them is I think they need a 4.5mm hole to work well in say brick/concrete/block. They have got me out of some tight spots with fixing in the bubbly super soft blocks... a liberal application of them screwed straight into the block can give a surprisingly secure fixing.
 
Problem I have with them is I think they need a 4.5mm hole to work well in say brick/concrete/block. They have got me out of some tight spots with fixing in the bubbly super soft blocks... a liberal application of them screwed straight into the block can give a surprisingly secure fixing.
Aha, so they do have another use!

For brick and block, there's a couple of things I found work well, if you don't want to use plastic plugs. Drill and plug with a 6mm wooden dowell, then just screw or nail the clip into the dowell. Gives a solid fixing, but obviously indoor only. Another option is drill a 4mm hole, then screw direct into the hole with a 5mm screw (can also do a 3mm hole with 4mm screw).

For those super soft aerated blocks, you can just hammer the 6mm dowells straight in without having to drill a hole.
 
I just use plasterboard fixings ( with the metal worms) to fix into plasterboard. If I'm using plastic trunking with D-line clips that fit inside the trunking, Wall dogs if it's a single cable or a p-clip as you see the worm.
Wall dogs are brilliant in block as sparkychick said.
 
I’m surprised one of the clip manufacturer hasn’t made a wall dog type metal buckle clip yet. Just screwinto the wall and lay the cable in place and fasten the buckle. No need for a separate clip...
 

Reply to Securing cables & trunking to prevent premature collapse. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
666
Related to another post, I am looking at running some network cable across a corridor above a false ceiling system. Is the ceiling support system...
Replies
8
Views
2K
Doing a EICR in a college…there have been many over the years, it’s approximately 50 years old & improvement happens every so often. The new...
Replies
23
Views
2K
The use of fire-resistant clips to avoid premature collapse of cables is obviously a good thing, but what about when the cables are in plastic...
Replies
7
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock