i have a mixer of breed floor run by a three phase asychnonous motor for which there is no nameplate .i measured the starting current(10A) and the nominal current (6A)
please help me to choose the right thermal overload relay for this
motor also the good brand name .
sincerly yours
mohamed riahi
 
Re: selecting the appropriate thermal overload relay for three phase asynchronous mot

i would use an overload with variable setting say 8A - 15A or thereabouts. try it at the lower setting and increase if necessary.
 
Re: selecting the appropriate thermal overload relay for three phase asynchronous mot

You usually size the protection to the run current, not the start current so maybe a 4-6A overload would be better. If you oversize it then it's possible for someone to come along in future and set it too high for it to be effective.
 
Re: selecting the appropriate thermal overload relay for three phase asynchronous mot

If you’ve measured the normal running current at 6A and the motor shows no sign of over heating, use this as the base for your selection. An overload with a range of 5 to 9A would suffice. I would recommend Telemecanique.
It’s difficult to make an accurate assessment / recommendation without the motor details.
 
Last edited by a moderator:
Re: selecting the appropriate thermal overload relay for three phase asynchronous mot

It’s nice when an OP gets back with a reply, iswiss has just PM’ed me with thanks.
 

Reply to selecting the appropriate thermal overload relay for three phase asynchronous motor in the Australia area at ElectriciansForums.net

Similar Threads

Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K
Hi just a question on setting the thermal overloads of a three phase motor. I have heard a few electricians state a few things regarding what it...
Replies
18
Views
6K
Y
Hi all, I'm new here so :flowers: I have a small industrial unit with three phase and single phase installed. The single is obviously for...
Replies
17
Views
3K
44ALLAN
4
K
Hi! I have a 3ph agitation motor Δ/Υ 0,42/0,24Α. I want to wire it as single phase using a permanent capacitor. Is there any way to calculate the...
Replies
16
Views
2K
Wazzajnr
W
W
as in the title can anyone help with selecting and setting the limit on a thermal overload relay, the motor is rated at 2.2 KW single phase, is it...
Replies
5
Views
11K
mayfair
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock