GBDamo

-
Esteemed
Arms
Reaction score
3,010
The electronics within our machines are manufactured to be tolerant of 220V +/-10%. many components have a max 250V allowance.

Now we all know that although our domestic supplies are supposed to be 230V they can vary widely, I personally have measured 257V on one supply.

What in your opinion is the most cost effective way of limiting the supply voltage without causing the to trip due to high voltage conditions.

This is to protect a single device (~3-5 Kw) not the entire installation.

Any useful ideas appreciated.
 
You equipment should be tolerable of the voltages of the market it sells into, it is common to see voltages 240v - 250v, also the equipment if it is prone to mains transients it should incorporate it's own protective measures.
Are these machines ones you build yourself or just machinery you have on site?

PS if you have measured 257volts on a meter with true rms then you should report the findings to DNO, this indicates there supply in in breach of their own regulations currently 253volts, if you have a cheap meter then be weary of the reading been accurate.
 
The electronics within our machines are manufactured to be tolerant of 220V +/-10%. many components have a max 250V allowance.

Now we all know that although our domestic supplies are supposed to be 230V they can vary widely, I personally have measured 257V on one supply.

What in your opinion is the most cost effective way of limiting the supply voltage without causing the to trip due to high voltage conditions.

This is to protect a single device (~3-5 Kw) not the entire installation.

Any useful ideas appreciated.
The electronics within our machines are manufactured to be tolerant of 220V +/-10%. many components have a max 250V allowance.

Now we all know that although our domestic supplies are supposed to be 230V they can vary widely, I personally have measured 257V on one supply.

What in your opinion is the most cost effective way of limiting the supply voltage without causing the to trip due to high voltage conditions.

This is to protect a single device (~3-5 Kw) not the entire installation.

Any useful ideas appreciated.
Voltage stabiliser, UPS
 
You equipment should be tolerable of the voltages of the market it sells into, it is common to see voltages 240v - 250v, also the equipment if it is prone to mains transients it should incorporate it's own protective measures.
Are these machines ones you build yourself or just machinery you have on site?

PS if you have measured 257volts on a meter with true rms then you should report the findings to DNO, this indicates there supply in in breach of their own regulations currently 253volts, if you have a cheap meter then be weary of the reading been accurate.

Thanks for the swift response, the equipment is "supposed" to be fit for purpose but we have one machine that is throwing up a protection fault code that indicates it has seen an overvoltage occurrence. This shuts the machine down and requires a manual reset. After multiple resets the fault becomes permanent and requires a replacement pcb.

We have two options in my mind, re-engineer to be more tolerant to overvoltage or install an up front voltage regulator but which product is best???

the Voltage was measured by a true RMS meter but not an expensive one.
 
With voltages measured that high I would first double check and get onto the DNO, last time I had 255v they were out within 2 hrs and came back next day to alter TX tapping, there is also the issue that this problem may not be a supply problem to your machine, there could be problems within your machinery that are spiking and blowing the PCB - if this is the case replacing the PCB will only possibly subject the new one to the same problems...
Without knowing what the machine is, its rating, how the PCB interacts with the rest of the machine etc it is impossible to advise on a solution as each scenario requires its own solution to suit. I take it your works in in close proximity to the sub station?
 
With voltages measured that high I would first double check and get onto the DNO, last time I had 255v they were out within 2 hrs and came back next day to alter TX tapping,

Like I said, it was an inexpensive meter..

....there is also the issue that this problem may not be a supply problem to your machine, there could be problems within your machinery that are spiking and blowing the PCB - if this is the case replacing the PCB will only possibly subject the new one to the same problems...

This is not only possible but quite likely, my request here is an attempt at grabbing a "low hanging fruit" solution. It may not be the most likely candidate but it is relatively cheap and easy to test hypothesis. Ruling out supply overvoltage gives a little more weight to to any push back we have with our supplier.

Without knowing what the machine is, its rating, how the PCB interacts with the rest of the machine etc it is impossible to advise on a solution as each scenario requires its own solution to suit. I take it your works in in close proximity to the sub station?

I can't go into too much detail but essentially the PCB manages/inverts the power to a compressor using a TRIAC array. The manufacturer is adamant that it is only a problem in the UK hence why i'd like to rule out supply voltage.

As for the sub station, of those that have shown this fault many have been very close to pole mounted transformers but not sub stations.

Thanks for your thoughs.
 
If it is indeed close to a Pole Tx then it is a likely suspect, l have known close proximity be an issue especially nuisance tripping of earth leakage devices, when you say close proximity are we talking meter or a few hundred. You may be getting unwanted transients so the first thing would be fitting an anti surge unit and also ensuring the voltage is within limits, if your meter is True RMS then it should be fine to rely on assuming you get it calibrated regularly, if unsure use 2 meters and if they agree it tends to mean they are correct.
As you cannot provide info on the machine I cannot offer other solutions but would a small VSD not be an option, these will usually have integral filters, Triac Arrays are fine and a cheap solution but they have their disadvantages but lack info to comment further and appreciate if you cannot disclose.
 
If it is indeed close to a Pole Tx then it is a likely suspect, l have known close proximity be an issue especially nuisance tripping of earth leakage devices, when you say close proximity are we talking meter or a few hundred. You may be getting unwanted transients so the first thing would be fitting an anti surge unit and also ensuring the voltage is within limits, if your meter is True RMS then it should be fine to rely on assuming you get it calibrated regularly, if unsure use 2 meters and if they agree it tends to mean they are correct.
As you cannot provide info on the machine I cannot offer other solutions but would a small VSD not be an option, these will usually have integral filters, Triac Arrays are fine and a cheap solution but they have their disadvantages but lack info to comment further and appreciate if you cannot disclose.
I know more info would make things easier so thanks for persevering.

By VSD do you mean voltage suppression device? and if so can you point me to a product that can handle 32Amp whilst clamping the output to 230/240V without tripping on overvoltage?
My googling has led me to £600-£1000 power conditioners but this seems like a massive sledgehammer for a tiny nut.
 
No, you express it runs a compressor so I make the assumption we are talking a motor, a VSD is a variable speed drive but i may be barking up the wrong tree here with the limited info', a drive would have built in filters usually and are more tolerant to input voltage ranges, it of course would mean altering the control of the machine and it would void any warranties and would have to meet machinery code standards.
 
..... The manufacturer is adamant that it is only a problem in the UK hence why i'd like to rule out supply voltage.
....
.
Are they comparing us to European 230 ... or usa 120 ?
Better dv/dt specced triacs are more expensive ...
So may be a price point thing ..while watching the pennies !
 
No, you express it runs a compressor so I make the assumption we are talking a motor, a VSD is a variable speed drive but i may be barking up the wrong tree here with the limited info', a drive would have built in filters usually and are more tolerant to input voltage ranges, it of course would mean altering the control of the machine and it would void any warranties and would have to meet machinery code standards.
Yes, replacing integral components is a no go for the reasons you state hence me looking for an upfront device.
 
Are they comparing us to European 230 ... or usa 120 ?
Better dv/dt specced triacs are more expensive ...
So may be a price point thing ..while watching the pennies !
EU 230V, as for the components we can only assume you're correct but to be honest we don't even know which exact component on the PCB is failing.
If I can guarantee the incoming voltage is 230+/-10% I can kick the fault back to the manufacturer. If clamping the voltage cures the fault then it's just a matter of retro-fitting a suitable device.
 
Your voltage is supposed to be 230v ?
But is it in reality ? Ours is officially 230v but in reality it is 240v.
But that is still within the official margin of +10%.
most electrical appliances will handle even 257v.
But some sensitive electronics may not.
So if your mains varies that much then don't use sensitive
electronics that cannot handle it.
Apart from using a UPS there is no easy way out !
What are you having a problem with ?
 
Do you recommend any particular products??
I could if it was 10 years earlier, but years go on and technology changes, maybe if you looked up UPs and VS companies, explain the scenario and conditions they will be able to advise you. That's what I did and got some good kit, it was used overseas in countries where the supplies weren't reliable, and had no trouble, the VS firm could also diagnose over the phone or by email, the UPs was EMERSON but that's all I remember, hope my reply has been useful, one thing the VS kit was dead simple to connect, loan and supply.

One thing I did find with the UPs, if you are using any form of remote controls or sensing equipment, use a screened cable or twisted pairs to try and avoid voltage pick up, I had one install where the UPs was in a small room which needed to be Air Conditioned, ( it was in Asia so very hot) the customer required an emergency stop for the UPs, which involved a control pair, every time the AC started up out would go the UPs, took me a while to suss out that the control pair was picking up volts from the AC starting and tripped the UPs, worth noting, I think my detective work caused the supplier to add the proviso in their install manual. Clever git aint I?
 
Last edited:
Stepping the voltage down with a bucking transformer is a simple and cheap solution if the maximum incoming voltage is high but the percentage variation is no more than the board's total tolerance. I.e., you don't need to stabilise, merely adjust your range of incoming voltages to align with the range the board will accept.

Suppose you find your supply only ever varies from 230-260V, while the board wants to see 207-253. You could reduce your midpoint 245V down to their midpoint 230V, making the max voltage 260-15=245V which is 8V within spec for the board, and your min 230-15=215V which is equally in spec. For a 3kVA device your bucking transformer has to knock 15V off the supply while handling 3000/215=14A, so a transformer of 15*14=210VA would do the job. In practice you would want to allow a bit more margin but you can get this for under £30 e.g. | 2 Output Toroidal Transformer, 225VA, 2 x 15V ac | - http://uk.rs-online.com/web/p/toroidal-transformers/6719034/

Primary across the mains, secondaries in parallel, in antiphase series with the load. Note that with a toroidal the secondaries may not be insulated from the exterior for the primary voltage - you might need to use extra insulating washers, or choose an EI-frame transformer instead. A regular autotransformer is ideal, especially if it has suitable taps to give you a bit of leeway, but the bucking method is usually by far the cheapest.

Note also that the board's method of measuring the voltage may not be the same as your true-RMS meter. It might have a basic method of measurement that is misreading high due to waveform distortion, even though your meter is giving a correct measurement.
 
Before throw large amounts of money at the problem I'd spend some time and effort establishing if there actually is one. I'd put a PQA on the supply and gather a few days or preferrable a week of data to establish the power quality and pinpoint precisely the issues.

Pointing a finger at power quality is a 'get out' that's often tried by suppliers to limit their warranty exposure when they're selling products that have high failure rates due to poor design or build quality. Having solid evidence will put the ball back in their court.
 
These domestic voltage regulators reduce voltage to 220V. You would need to check their specification to see if they can maintain this regulation for the power you intend to draw through it.

Energy Ace Voltage Optimizer | Single Phase | ExpertElectrical.co.uk - https://www.expertelectrical.co.uk/circuit-protection/energy-ace-voltage-optimizer?fee=3&fep=18383&gclid=EAIaIQobChMI7ffOx5rU1wIV7pPtCh26bg6hEAQYBSABEgIQ-vD_BwE

Eco-Max Home Voltage Optimisation 63 Amps - https://www.savemoneycutcarbon.com/product/eco-max-home-voltage-optimisation-63-amps/?gclid=EAIaIQobChMI7ffOx5rU1wIV7pPtCh26bg6hEAQYASABEgLkmfD_BwE

This one below regulates at preset 220V for power consumption up to 2.5kW permanently and up to 4.5kW for about 10-20 minutes and then switches to bypass to output the prevailing mains voltage:

VPhase Voltage Optimiser | REUK.co.uk - http://www.reuk.co.uk/wordpress/energy-efficiency/vphase-voltage-optimiser/
 

Reply to Sensitivity to high voltages in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Thanks to being quarantine for a week i finally managed to have a go at the the practice exams in the course and i have a few questions for the...
Replies
23
Views
3K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock