Say you had to feed power to a shed/detached garage in the UK with a sub unit inside it. How would you go about the earthing? What earthing arraignments can be used at the shed if the home is:

TN-S
TN-C-S
TT

And do you always need an earth rod at the shed?
 
Say you had to feed power to a shed/detached garage in the UK with a sub unit inside it. How would you go about the earthing? What earthing arraignments can be used at the shed if the home is:

TN-S
TN-C-S
TT

And do you always need an earth rod at the shed?

The earthing arrangement used would normally be whatever the incoming supply is, for a domestic shed there is rarely a need to create a seperate TT earth.

If there are any extraneous conductive parts in the shed then the cpc of the distribution circuit will need to be big enough to provide main bonding.
If this is not possible then that is when a TT system seperate from the house installation would need to be created. The largest main bond normally required in domestic is 10mm so its not usually a problem to provide a main bond at a shed if required.

On larger installations it could be prohibitively expensive to run a main bond to a seperate building and so a TT earth would be set up there.
For example if a small outbuilding has a 10mm supply cable but the installation requires 50mm main bonding it could be prohibitively expensive to run a main bond to it.
 
I see.

This video has me curious. It looks like he isolated the SWA armor and then made a separate TT earthing system at the workshop?
View: https://youtu.be/Pxrz1oFFEXE?t=1481

I haven't looked but he probably does, just because someone has posted a video on YouTube it doesn't mean they know what they are doing.

There are a lot of people in this country who will follow what their mate in the pub told them rather than reading and understanding the regulations.
 

Reply to Shed Feed (Hypothetical) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
I’m planning on putting in a small (10x10) detached shed for garden storage plus a freezer for meat storage, an in-wall AC unit (for temperature...
Replies
9
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock