Hi,

I know this is a very commonly debated topic, but I have never found a solution agreed by a majority.

I am in the process of building a wooden shed, approximately 20metres from the house (up to 30 metre cable run to the CU and meter cut out). I have a PME/TNCS supply to the property and no extraneous metallic services/structures in the shed. I would like to install a handful of IP rated sockets both inside and to the exterior of the shed, along with an interior LED light and a couple of LED floodlights/bulkhead lights outside (it will be next to my patio/seating area).

My proposal is to install a 40A RCBO, supplying a glanded SWA cable (earth connected to house CU earth). The SWA will be ducted (to allow replacement-I'm thinking of the long term as I don't intend on moving again, and to allow provision of other services possibly). This SWA would then enter the shed and terminate in to a garage type CU with RCD mainswitch, one 20a MCB for sockets and a 6a MCB for my lighting requirements. I propose not to connect the earth of the SWA to the shed CU so as not to export the earth, but instead use a sufficiently deep enough earth rod (depth dependent on testing of course) and connect this to the shed CU via a 10mm earth cable to provide a local TT arrangement.

My question is, does this seem the safest way of installing such a shed supply? I realise that most people wouldn't duct the SWA, etc. but as I am doing the garden up, it's my own house and I do not intend on moving, I wish it to be future proof (able to replace SWA if ever necessary, etc.) Likewise, I would prefer to have a separate CU in the shed to allow future increased loads, although initially there will be no, "heavy duty" workshop tools/high current loads.

Would I be better using a time delay RCBO at the house to allow discrimination between that and the house RCD? Would I be best terminating the SWA in to a plastic enclosure prior to the shed CU to ensure the SW does not touch and
innadvertantly earth the shed CU?

I'm used to working on industrial, rolling stock based installations, rather than domestic installations, so please excuse any question that may seem obvious!
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
  • Thread Starter Thread Starter
  • #2
With regard to the time delayed RCBO; my thinking was just incase the steel wire of the earth came in to contact with the localised TT system, though on hindsight it is probably overkill!!
 

buzzlightyear

-
Arms
Esteemed
Basic requirements for earthing and bonding
Where an installation serves more than one building, main protective bonding is required in each building served, except for a building where there are no extraneous-conductive-parts, such as metallic water, gas or oil installation pipes (Regulation 411.3.1.2 refers).

Option 1: Extending the earthing and bonding system



The image shows an example of the earthing and bonding arrangements where the installation in a house is extended to serve a detached outbuilding. A Building Earth Marshalling Terminal (BEMT) is usually provided in the outbuilding to marshal together the main bonding conductor(s), if any, and the circuit protective conductors (cpcs) in that building. The BEMT must be connected to the MET by:

• the cpc of the distribution circuit supplying the outbuilding, and

• a main bonding conductor, if there are any extraneous-conductive-parts at the outbuilding.

As shown, the functions of the cpc and main bonding conductor (if any) may be combined in a single protective conductor having a cross sectional area (csa) meeting the requirements for both functions.



Option 2: Making the installation in the detached outbuilding part of a TT system with its own installation earth electrode and MET



The image shows an example of the earthing and bonding arrangements where an installation in a house supplies an installation in a detached outbuilding, forming part of a TT system with its own installation earth electrode and MET. It is desirable for there to be no connection between the earthing and bonding arrangement of the installation in the outbuilding and that of the installation in the house (such as through a protective conductor or shared metallic pipeline), as shown.

Note: Although both options show an earthing facility provided by the distributor being used as the means of earthing (TN-S or TN-C-S system), the earthing conductor could be connected to an installation earth electrode instead (TT system).



Table 1 – Sizing requirements for cpc and main bonding conductor



Note. The requirements of Regulation 544.1.1, referred to in Table 1, can result in a main bonding conductor size greater than that of the live conductors or cpc of the distribution circuit supplying the outbuilding, particularly where PME conditions apply (TN-C-S system).

Table 1 summarises the requirements of BS 7671 for sizing the cpc and main bonding conductor to the outbuilding. If the functions of these two conductors are combined in a single protective conductor, this must have a csa not less than that required for either function. Where there is no such connection, the main requirements of BS 7671 applying to the earthing and bonding are as summarised in Table 2.



Table 2 – Requirements where the outbuilding installation forms part of TT system with no connection to the earthing and bonding arrangements of the house installation:

A further consideration applies where there is a connection between the earthing and bonding arrangement of the detached outbuilding and that of the installation in the house, if the latter installation forms part of a TN-C-S system where PME conditions apply.

Where this is the case, PME diverted neutral current may flow in the connection between the two earthing and bonding systems. To avoid harmful thermal effects caused by this current, the csa of this connection and of the main bonding conductors and the earthing conductor of the installation in the outbuilding needs to meet with the requirements for a main bonding conductor of the installation in the house (which are summarised in Table 1).
 

Spoon

-
Mentor
Arms
Esteemed
My proposal is to install a 40A RCBO, supplying a glanded SWA cable (earth connected to house CU earth).
Could just use a 40A breaker as the SWA does not need RCD protection. This will also remove the discrimination needed with the RCD in the shed.
What size ducting are you thinking of?
If you are thinking of increasing the load in the shed in the future why not install a bigger cable now, saving money and time in the future?
 
  • Thread Starter Thread Starter
  • #5
Thank you Buzzlightyear, it is very much appreciated and confirms my plans on a localised TT arrangement to the shed.

Would you have a preference over either method? I can see that a localised TT system to the shed could suffer from degradation of the earthing arrangements, i.e. earth rod corroding, ground conditions affecting earth impedance, etc.
 
  • Thread Starter Thread Starter
  • #6
Thanks for that suggestion Spoon; I had presumed that RCD protection was required for any external circuit. I obviously stand corrected!!

I'm not sure on ducting size yet to be honest. I have no plans as such to increase the load, but just thinking of the future. I don't fancy spending £1000's doing the garden and Mrs Ashton asking for a hot tub next to the shed in 5 years time. Cue many cursed words and me ripping up the turf and patio!!
 

Spoon

-
Mentor
Arms
Esteemed
How about price up the difference between 10mm and 16mm.
I bet the price of 16mm is a lot lower than 10mm and ducting.
You should not need more than 50A for a shed.
 

Spoon

-
Mentor
Arms
Esteemed
I'm an industrial guy as well. This forum is cool as you can learn a hell of a lot from it. Some very knowledgeable people on here.
 

Spoon

-
Mentor
Arms
Esteemed
Some very knowledgeable people on here.
has Pete and Tele fallen sleep in there chairs .Lol.
Funnily enough, they are who I was thinking of, when typing that. Of course there are many more people who also fit the bill.


Not very good English, but it seems my brain can't be arsed switching on today...
 
  • Thread Starter Thread Starter
  • #14
Thank you Buzzlightyear. Can I assume your preference would be a localised TT earthing arrangement (through an earth rod) for the shed then, rather than exporting? I shall let you all have a laugh (read: look). Glad to see you have confidence!

You're quite right about the excellent knowledge on here; every day is a learning day as they say Spoon. The idea of 16mm and no ducting probably is the better option long term.

Funny you should mention insulation; it actually is! No Bob Hope here though; the railways are quite strict on the old drugs and alcohol!!
 

Spoon

-
Mentor
Arms
Esteemed
This is where the more knowledgeable people people can correct me but would it be easier to export the earth than use TT for this length of circuit?
 

DPG

-
Arms
Esteemed
Patron
Using a good reliable existing earth sounds better than a hopeful earth rod banged in next to the shed.
 
  • Thread Starter Thread Starter
  • #18
Always thought it would be interesting work, working on the railways. Is it?
I work on the Ballast Cleaning System; it's a massive train that excavates the track ballast, screens it the poor ballast and puts the ballast and track back, adding any additional ballast as required. It's a pretty impressive machine and one of the longest trains on the network (over half a mile long!) I love my job, but hate living out of a hotel and the often unsocial and long working hours.

Using a good reliable existing earth sounds better than a hopeful earth rod banged in next to the shed.
I always thought that DNO's took issue with exporting of the earth. I had planned on testing it of course. I would prefer to use the existing earth if possible, as you rightly say, it would be better to use a known good earth.
 

davesparks

-
Mentor
Arms
Esteemed
Presumably this is going to be a minimum of 10mm SWA, so why not just install a 3 core and use the DNO provided earth?

10mm 3 core gives you a cpc large enough to provide bonding to anything that may need it now or in the future.
 

davesparks

-
Mentor
Arms
Esteemed
I always thought that DNO's took issue with exporting of the earth. I had planned on testing it of course. I would prefer to use the existing earth if possible, as you rightly say, it would be better to use a known good earth.
You can extend the equipotential zone to wherever you like, as long as you do it properly there is no problem.
 
  • Thread Starter Thread Starter
  • #22
Thanks Davesparks, that had been my preferred method if at all possible. As luck would have it, I spoke with a friend who works for the local DNO and he has confirmed exactly what you have just mentioned. I also spoke with another friend who has some 4-core 16mm SWA and 110mm twinwall ducting as an off-cut (he works on large private network installations and 25m is an "off cut" for them. I know the ducting is a bit over kill, but it's free, so why not!?

My intention is to use a none RCD protected MCB currently in the CU, utilising the 16mm SWA to supply an RCD-protected, small garage type consumer unit with a MCB for the sockets, and a MCB for the lighting. I will use the 3rd core as suggested. Hopefully I can take the SWA straight to the house CU, but I have a feeling that I will need to terminate the SWA and continue the supply in T+E back to the CU. Unfortunately, the house's CU is back in the centre of the house in an understairs cupboard.

It's staggering that the myth about sheds and PME/TNCS still persists.
Working on rolling stock, I have never really had much need to investigate this myth, I just remember hearing it mentioned on these sorts of forums in yesrs gone by.
 
  • Thread Starter Thread Starter
  • #24
Well with a 4 core 16mm SWA Lewis in the case of your job you could have a 32mm2 CPC if you wanted !
Indeed Dave OCD! Might as well use it if it's available! Should certainly provide a much better solution than the earth rod.

Thank you everyone for your help and input!
 

davesparks

-
Mentor
Arms
Esteemed
My intention is to use a none RCD protected MCB currently in the CU, utilising the 16mm SWA to supply an RCD-protected, small garage type consumer unit with a MCB for the sockets, and a MCB for the lighting. I will use the 3rd core as suggested. Hopefully I can take the SWA straight to the house CU, but I have a feeling that I will need to terminate the SWA and continue the supply in T+E back to the CU. Unfortunately, the house's CU is back in the centre of the house in an understairs cupboard.

[\QUOTE]

Converting to T&E may put you back at square one with the need for an RCD for the submain depending on how it is installed/routed.

The 'best' way to do it, in my opinion, would be to run the SWA back to the CU location and fit a switch fuse to protect it rather than an mcb.
 
  • Thread Starter Thread Starter
  • #26
My thoughts exactly Dave. The more I look at the cable route through the house, the more I think it will be difficult. Unfortunately, the downstairs floor is solid concrete though. I should be able to SWA right up to the external wall and then terminate in to an IP box and run T+E under the upstairs floor and back down to the top of the cupboard where the CU is located. I am able to install it in trunking/conduit.

Alternatively there is a redundant piece of SWA which runs from the adjacent wall to the C.U., across the garage ceiling joists, down the side of the garage, under the decking to an outside IP box to provide a supply to the conservatory (I don't know why they did it that way either, so don't ask!!) That's now redundant now the conservatory is on the ring, so I could potentially use that, depending on it's size, integrity, etc. but it's routing is not ideal (looks like it's just chucked straight under the decking!)

I shall investigate further when I'm home, and let you all know the outcome/finished product.
 

Top Cat

-
Arms
Basic requirements for earthing and bonding
Where an installation serves more than one building, main protective bonding is required in each building served, except for a building where there are no extraneous-conductive-parts, such as metallic water, gas or oil installation pipes (Regulation 411.3.1.2 refers).

Option 1: Extending the earthing and bonding system



The image shows an example of the earthing and bonding arrangements where the installation in a house is extended to serve a detached outbuilding. A Building Earth Marshalling Terminal (BEMT) is usually provided in the outbuilding to marshal together the main bonding conductor(s), if any, and the circuit protective conductors (cpcs) in that building. The BEMT must be connected to the MET by:

• the cpc of the distribution circuit supplying the outbuilding, and

• a main bonding conductor, if there are any extraneous-conductive-parts at the outbuilding.

As shown, the functions of the cpc and main bonding conductor (if any) may be combined in a single protective conductor having a cross sectional area (csa) meeting the requirements for both functions.



Option 2: Making the installation in the detached outbuilding part of a TT system with its own installation earth electrode and MET



The image shows an example of the earthing and bonding arrangements where an installation in a house supplies an installation in a detached outbuilding, forming part of a TT system with its own installation earth electrode and MET. It is desirable for there to be no connection between the earthing and bonding arrangement of the installation in the outbuilding and that of the installation in the house (such as through a protective conductor or shared metallic pipeline), as shown.

Note: Although both options show an earthing facility provided by the distributor being used as the means of earthing (TN-S or TN-C-S system), the earthing conductor could be connected to an installation earth electrode instead (TT system).



Table 1 – Sizing requirements for cpc and main bonding conductor



Note. The requirements of Regulation 544.1.1, referred to in Table 1, can result in a main bonding conductor size greater than that of the live conductors or cpc of the distribution circuit supplying the outbuilding, particularly where PME conditions apply (TN-C-S system).

Table 1 summarises the requirements of BS 7671 for sizing the cpc and main bonding conductor to the outbuilding. If the functions of these two conductors are combined in a single protective conductor, this must have a csa not less than that required for either function. Where there is no such connection, the main requirements of BS 7671 applying to the earthing and bonding are as summarised in Table 2.



Table 2 – Requirements where the outbuilding installation forms part of TT system with no connection to the earthing and bonding arrangements of the house installation:

A further consideration applies where there is a connection between the earthing and bonding arrangement of the detached outbuilding and that of the installation in the house, if the latter installation forms part of a TN-C-S system where PME conditions apply.

Where this is the case, PME diverted neutral current may flow in the connection between the two earthing and bonding systems. To avoid harmful thermal effects caused by this current, the csa of this connection and of the main bonding conductors and the earthing conductor of the installation in the outbuilding needs to meet with the requirements for a main bonding conductor of the installation in the house (which are summarised in Table 1).
F me! did you swallow the reg's book!:)
 

Spoon

-
Mentor
Arms
Esteemed
I should be able to SWA right up to the external wall and then terminate in to an IP box and run T+E under the upstairs floor and back down to the top of the cupboard where the CU is located.
Just be aware that the T+E may need RCD protection, if you do it this way.
 
  • Thread Starter Thread Starter
  • #30
Just be aware that the T+E may need RCD protection, if you do it this way.
Am I correct in thinking that only RCD protection is required on the submain if it is in a wall and to a depth of 50mm or less? I can mechanically protect the run with galvanised trunking or similar (straight run across the floor and then a short 600mm run down the wall to the CU. Just not sure if I can achieve the bend radius to get the SWA up the side of the house, in beneath the ceiling/floor void and then down the wall. I'll have a proper look when I'm home and see which methods are possible with regard to cabling.
 

ipf

-
Mentor
Arms
Esteemed
FFS.….it's a shed with a few sockets and a few led lights with no other services.
I'd be very surprised if the load is going to be anywhere near 30 amps. Get a run of 6mm 3 core swa, from main CU to shed CU, put in from a 32A mcb. No jointing, easy to run and no rcd protection needed, except at the shed.

Unless you're thinking of putting in a hot tub or sauna,
that is.;)
16mm 4 core.....you could feed a decent size indoor swimming pool with that...
 
Last edited:
  • Thread Starter Thread Starter
  • #32
FFS.….it's a shed with a few sockets and a few led lights with no other services.
I'd be very surprised if the load is going to be anywhere near 30 amps. Get a run of 6mm 3 core swa, from main CU to shed CU, put in from a 32A mcb. No jointing, easy to run and no rcd protection needed, except at the shed.

Unless you're thinking of putting in a hot tub or sauna,
that is.;)
16mm 4 core.....you could feed a decent size indoor swimming pool with that...
IPF, I thought I mentioned it in an earlier post, but maybe not: I'm trying to future proof the installation and the Mrs Ashton does keep mentioning a hot tub. I know the 16mm is overkill, but it is free and I'm a tight Yorkshireman. :laughing:

I might just go with the original idea of ducting it (also got some available for free!) And use the smaller SWA.....even if I do have to buy it. :laughing: At least if Mrs Ashton decides on a hot tub eventually, it doesn't mean ripping up the garden!
 

ipf

-
Mentor
Arms
Esteemed
IPF, I thought I mentioned it in an earlier post, but maybe not: I'm trying to future proof the installation and the Mrs Ashton does keep mentioning a hot tub. I know the 16mm is overkill, but it is free and I'm a tight Yorkshireman. :laughing:

I might just go with the original idea of ducting it (also got some available for free!) And use the smaller SWA.....even if I do have to buy it. :laughing: At least if Mrs Ashton decides on a hot tub eventually, it doesn't mean ripping up the garden!
Fair enough, Lewis. 16mm 4core will be difficult to work with and is real over kill. Even future proofing, 10mm 3 core will suffice, easily, and you wont find many more problems installing that rather than 10mm T+E, plus you've got your 10mm earth for bonding. Use a m/clad adaptable box or isolator, next to the CU for termination, if you have problems terminating directly.
Good luck and let us know how you go on with it.

edit. PS...….tight yorkie t*** ;)
 
Last edited:
  • Thread Starter Thread Starter
  • #34
Duly noted IPF, and I know that you are right and I should really dip my hand in my pocket and just buy the 10mm 3core (found 25metres for around £80 online which doesn't seem too bad). My "back of a fag packet" calculations give me a load of up to 60A before I would need to worry about cable size. Even a couple of sockets, some lights and the fanciest hot tub Mrs A can find isn't going to pull more than 60A.

I should be good on the SWA termination at the CU; I got a good deal on one of the large Schnieder CU's when the house was rewired. So much easier to work with than some of the poxy little CU's you find!

I just hope she doesn't see your post about a swimming pool.....she may get ideas. :weary:

I shall let you know how I get on with it; it'll be a few weeks yet. I'm just recovering from putting up 30 odd bays of concrete post & gravelboard fencing, and on day 5 of 12 at work. :confounded:

Thanks for your clear and concise suggestions IPF; it is very much appreciated.
 