Hi all

I have a situation that I can't get my head around and hoping someone can help!

A client reported receiving shocks from her shower. When I visited the property, and when wet if you touched the metal parts of the shower (which was not electric), and the bath taps at the same time you got quite a shock from it.

There was no earthing system installed to the property. Nor was there water bonding or gas bonding.

They didn't want to get a TNCS system installed despite my recommendations, and asked me to install an earth rod which I did (ze 109 ohms). I also installed gas and water bonding. RCD protection to all circuits.

However, we still experienced the shock even with the earthing installed.

I did a bit of fault finding and turns out an 'unknown' circuit on a 6a MCB was causing the problem. When I disconnected the circuit, no more shocks from the shower/taps.

I thought installing an earth rod and water bonding would have stopped the shocks - am I wrong?

Grateful for any input. Kelly x
 
Hi all

I have a situation that I can't get my head around and hoping someone can help!

A client reported receiving shocks from her shower. When I visited the property, and when wet if you touched the metal parts of the shower (which was not electric), and the bath taps at the same time you got quite a shock from it.

There was no earthing system installed to the property. Nor was there water bonding or gas bonding.

They didn't want to get a TNCS system installed despite my recommendations, and asked me to install an earth rod which I did (ze 109 ohms). I also installed gas and water bonding. RCD protection to all circuits.

However, we still experienced the shock even with the earthing installed.

I did a bit of fault finding and turns out an 'unknown' circuit on a 6a MCB was causing the problem. When I disconnected the circuit, no more shocks from the shower/taps.

I thought installing an earth rod and water bonding would have stopped the shocks - am I wrong?

Grateful for any input. Kelly x

You need to trace the "unknown circuit" and rectify the fault Kelly
 
Yeah.... errr... thanks for that Pete. I did trace the unknown circuit, but it doesn't supply anything we can find inside or outside the property. So she was happy for me to disconnect it. Aside from ripping up the floorboards and opening up her walls I don't know how you would trace it and repair.

Thanks for your input, but I didn't actually ask what I should do. I asked why she was still receiving shocks when earthing was all installed.

I was wondering if it was because the earth was not good enough, or the earth leakage was very high and if that can happen.
 
I would physically disconnect the circuit let them know to report anything that no longer works to contact you, if a waste of time and money chasing ghost circuits if they can just be disconnected.

Look at the fault as a possible 2 way system as its very easy to look at it as going the obvious route but it could be possible the fault is actually in reverse in effect the tap may be live and your grounding it through the shower plumbing and not vice versa.
 
Last edited:
Could be fault in cable buried in wall, live penetrated by nail or screw into wall. Shower outlet, could be picking up fault in buried pipe work in adjacent wall. With the faulty circuit reconnected, does it cause your new installed RCD to trip when touching shower & bath taps (using trailing lead, not human contact!)?
 
'valleybilly' is along the right lines, do a long lead test to the furtherest point of the plumbing, I had a similar problem to this with a water softner connected connected across the mains and no continuity across the water softner, fixed it with 2 * earth clamps and a bit of 10mm.
 
This reminds me of a fault i had Many years ago I was called to a similar situation. TNS system, customer was getting shocks off taps and pipes in a ground floor shower room. Carried out earth tests and found all pipe work was nicely earthed. After some head scratching we determined the floor was live and the Customer was earthing them selfs out on the pipe work.

We managed to get about 100v measured from the floor to a known earth, when we turned off the consumer unit it was still there.

After some more tests we finally traced it to a old lead cable going to the next door neighbours shed. Disconnected this and all was good. Thankfully they were ok with this.

The problem you have seems similar, a damaged live does not always have to go to a good enough earth to trip something. Even with RCD's
 
strange why the rcd isnt tripping

The fault current is less than that required to trip the 30ma RCD.

I've only ever had 1 shock on an RCD protected circuit, it hurt and didn't trip, although the RCD later tested as O.K.

The O.P fault will have continuity between the Bath tap and the Live to the unknown circuit and as Valleybilly said above the tap and pipework won't be bonded.
The shower is the earth.
 
Last edited:
Ok question I thought limiting the current that's flows through your body. Ie 30 mili amp Is safe The op says people are getting tingles of the pipe and taps my question is what value ie mili amps would we actually get tingles from
 
30mA is not safe, it is a level at which about 90-95% of the population will not die from experiencing.

1 mA Barely perceptible
16 mA Average “let go” threshold
20 mA Difficulty breathing
100 mA Heart “flutter” threshold
2 A Heart stoppage and internal organ damage
15/20 A ADS (average) opens circuit

Effects of current and time are shown in this graph within the AC-2 range, which is what we will mainly be concerned with regarding RCD protection, this varies from "Am I getting tingles" to "ouch that really hurt", but you will still have the chance to think this!
Shock physiological time mA.jpg
 
30mA is not safe, it is a level at which about 90-95% of the population will not die from experiencing.

1 mA Barely perceptible
16 mA Average “let go” threshold
20 mA Difficulty breathing
100 mA Heart “flutter” threshold
2 A Heart stoppage and internal organ damage
15/20 A ADS (average) opens circuit

Effects of current and time are shown in this graph within the AC-2 range, which is what we will mainly be concerned with regarding RCD protection, this varies from "Am I getting tingles" to "ouch that really hurt", but you will still have the chance to think this!
View attachment 28887

....I'm really worried about what you do in your cellar...:smile5:
 

Reply to Shocks when touching shower thermostat controller and bath taps in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
196
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
418
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock