Hi. I'm a new user to this forum, and would appreciate if you could help me out on this one.
i need to price a job on a new shower block. Customer has just had new three phase supply. Shower block is 100metres away from DNO cut out.
I was thinking of
4 pole 300ma TD RCD in an insulated enclosure
100A metal fused switch disconnector TP&N
100m of 25mm 4 core SWA cable
square d 3 phase db with 125a main switch
Can anyone suggest a good, spacious Insulated rcd enclosure?! Also, does anyone see any problems with this setup!?
Thanks for your help