There seems to be a lot of ambiguity and difference of opinions on the Forum regarding shower cable sizing. I have one to fit, 9.7Kw through a seperate RCCB and 50a MCB shower unit via a Henley block using 16mm tails. @ 11m run - 6m capped trunking, 3m under floorboards and 2m clipped direct in the loft [is this Ref. method 'B' or 'C' or an average of the two?]no insulation or grouping. 4D5 table for C gives 47a = 6mm. Manufacturer advises max of 45a but does not stipulate size. Irrespective of possible future events, whats wrong using 6mm?
 
Without taking into account any other factors your cable will have to be rated above 50A as you have stated you are using a 50A mcb for overcurrent protection.
 
It's no different to any other fixed load. The cable rating must exceed the rating of the protective device taking into account installation methods rating factors,and the maximum volt drop must not be exceeded.
 
The size of cable will all depend on the lenght of run and diffrent factors.
You will need a 10mm T&E, as one of the other posts said, a 50A breaker is too large for a 6mm cable.
 

Reply to Shower cable sizing in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock