hi guys

Customer wanting to upgrade electric shower.

6MM twin and earth to isolator then to shower total length of cable run 7 meteres, this including run to shower.

This is protected by an RCD and being currently on 32A cb.

Can this wire stop in if wanting a 10.8KW shower?

Have tested the circuit and all is good.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
B

bigal

  • Thread Starter Thread Starter
  • #2
Keep it on a 32 amp mcb. If it holds in it's good and creates no danger. Chances are it will pop out often 'cause it's pushing the boundries. 10500/230 = 45.6 amps. 10 mm if it's a problem. You are an electrician, not a magician.
Bigal
 
hi guys

Customer wanting to upgrade electric shower.

6MM twin and earth to isolator then to shower total length of cable run 7 meteres, this including run to shower.

This is protected by an RCD and being currently on 32A cb.

Can this wire stop in if wanting a 10.8KW shower?

Have tested the circuit and all is good.
I have tried this and works ok BUT it works MUCH better with the bigger cable.Must be less voltage drop or something.The one I had doings with was about 16m away and after new cable went in there was far better force of hot water,with the 10mm.With the 6mm whenever you turned up the temp the pressure dropped.Buggered if I know why but that is what happened.
 

slocm3105

-
Arms
I have tried this and works ok BUT it works MUCH better with the bigger cable.Must be less voltage drop or something.The one I had doings with was about 16m away and after new cable went in there was far better force of hot water,with the 10mm.With the 6mm whenever you turned up the temp the pressure dropped.Buggered if I know why but that is what happened.
Well when u turn up the temp, you in turn are drawing more current therefore causing that 6mm cable being pushed at its boundaries to get hotter, thus increasing resistance, and to put it plainly this induces voltage drop. Therefore your shower was not getting the required power to run effectively.
 
G

Guest123

  • Thread Starter Thread Starter
  • #5
Sorry I may have missed the point here:confused:

10800/230 = 46.956A with no diversity allowable on showers.

What is the point in leaving it on 6mm protected by 32A MCB when plainly you will have no end of problems with it.

Upgrade to 10mm and 40A MCB to start with.

Also why do you want such a high current rating shower?? mine is 8.5KW and is more than adequate.

Cheers.
 
R

rapier

  • Thread Starter Thread Starter
  • #6
Also why do you want such a high current rating shower?? mine is 8.5KW and is more than adequate.

Cheers.
Not my doing mate them customers:mad:

I did advice lowering rating of show but you know customers will have further chat with them.

What rating CB is urs on lenny.

Cheers 4 now guys
 
Last edited by a moderator:
G

Guest123

  • Thread Starter Thread Starter
  • #7
Hey buddy.

My 8.5KW is wired in 10mm and on 40A.

To be honest I dont use 6mm for showers at all anymore only 10mm

Cheers.
 
Last edited by a moderator:
S

Spudnik

  • Thread Starter Thread Starter
  • #8
Dont forget that electric showers are fairly dependent on incoming mains pressure so a low KW shower may well work better in one area than another.
 
Hey buddy.

My 8.5KW is wired in 10mm and on 40A.

To be honest I dont use 6mm for showers at all anymore only 10mm

Cheers.
me too,10mm split concentric I use.Far handier than T&E,only have to drill a smaller hole in the joists,can even clip it surface up the side of a house and into the eves,its got a full sized cpc and you can buy cut lengths of it from the wholesaler.:)

Not my doing mate them customers:mad:

I did advice lowering rating of show but you know customers will have further chat with them.

What rating CB is urs on lenny.

Cheers 4 now guys
If you do go 10kw dont forget as well as the 50amp mcb you will need a 50amp pull cord switch as well.
 
Last edited:
S

sivoodoo

  • Thread Starter Thread Starter
  • #10
10mm split concentric, how much per meter on average?
 

ian.settle1

-
Mentor
Arms
Well when u turn up the temp, you in turn are drawing more current therefore causing that 6mm cable being pushed at its boundaries to get hotter, thus increasing resistance, and to put it plainly this induces voltage drop. Therefore your shower was not getting the required power to run effectively.

Not always true on some showers as when you have it set to the high setting you will be taking the maximum current, when you turn the other control knob all you are doing is opening and closing a valve on the water going throught the shower and not the current.
 

Reply to Shower circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net